So I went to look at a job today in an engineering workshop. They are stripping out the existing machinery and having a reshuffle.

The bus bars are being altered to suit the new arrangement.

The bus bars are fed from a 6 way panel board which was installed in the 1960's.

Would you suggest upgrading the panel board as isolators for it are now obsolete and so old? Ill post some pictures in a bit.

I'm thinking that the existing isolators won't meet current disconnection times etc but don't have any info on it other than the photos.

Many thanks
 
[ElectriciansForums.net] New panel board required?


Hold on fella give me a minute
 
So I went to look at a job today in an engineering workshop. They are stripping out the existing machinery and having a reshuffle.

The bus bars are being altered to suit the new arrangement.

The bus bars are fed from a 6 way panel board which was installed in the 1960's.

Would you suggest upgrading the panel board as isolators for it are now obsolete and so old? Ill post some pictures in a bit.

I'm thinking that the existing isolators won't meet current disconnection times etc but don't have any info on it other than the photos.

Many thanks

What do you mean the isolators won't meet disconnection times? Why does it matter what time an isolator disconnects in? An isolator is by definition an off-load device after all.
 
What do you mean the isolators won't meet disconnection times? Why does it matter what time an isolator disconnects in? An isolator is by definition an off-load device after all.
Isolators have a AC-rating which relates to their ability to switch different kinds of loads from resistive to inductive of different natures ... you comment to say isolators are off load switching devices is incorrect, look at the AC code of a main switch in a consumer unit which is rated for resistive and slightly inductive load switching.

PS .... yes some isolators state no load switching which is where you get your post from and this will be reflected in their AC rating...
 
Isolators have a AC-rating which relates to their ability to switch different kinds of loads from resistive to inductive of different natures ... you comment to say isolators are off load switching devices is incorrect, look at the AC code of a main switch in a consumer unit which is rated for resistive and slightly inductive load switching.

PS .... yes some isolators state no load switching which is where you get your post from and this will be reflected in their AC rating...

Ok, I am happy to stand corrected if I am wrong but I was taught that:
Isolator = off load device designed to disconnect from the source of supply, also called disconnectors
Switch = on-load device designed to switch the supply to control a load.
The above can be combined in the same unit to become isolating switches / switch disconnectors.

So your example of a main switch in a consumer unit is normally listed as being a switch-disconnector by manufacturers, it fulfills both roles.
 
Ok, I am happy to stand corrected if I am wrong but I was taught that:
Isolator = off load device designed to disconnect from the source of supply, also called disconnectors
Switch = on-load device designed to switch the supply to control a load.
The above can be combined in the same unit to become isolating switches / switch disconnectors.

So your example of a main switch in a consumer unit is normally listed as being a switch-disconnector by manufacturers, it fulfills both roles.

I was taught exactly the same thing.

Although I was also taught that an isolator would trip under fault conditions! lol
 
Not as far as we have been led to believe I'm afraid the idea is in the title. It's all about load shedding. There is no issue with turning off the switch disconnector with all the loads applied however you must not re energise it with all the loads applied or you run the risk of blowing it. That's why it's called a switch disconnector. Personally I would always load shed both ways.
 
Not as far as we have been led to believe I'm afraid the idea is in the title. It's all about load shedding. There is no issue with turning off the switch disconnector with all the loads applied however you must not re energise it with all the loads applied or you run the risk of blowing it. That's why it's called a switch disconnector. Personally I would always load shed both ways.

Wtf? breaking load current is a hell of a lot more onerous on a switch than making onto a load.

It is called a switch disconnector as it combines the functions of both a switch and a disconnector (isolator)
 
Ok, I am happy to stand corrected if I am wrong but I was taught that:
Isolator = off load device designed to disconnect from the source of supply, also called disconnectors
Switch = on-load device designed to switch the supply to control a load.
The above can be combined in the same unit to become isolating switches / switch disconnectors.

So your example of a main switch in a consumer unit is normally listed as being a switch-disconnector by manufacturers, it fulfills both roles.


In your defense here the terminology has slightly changed over the years I was taught 'load break switch' but now you can buy variants on Isolators, disconnectors and switches with the specified AC-rating which goes against what even I was taught hence I corrected you but yes generally what you say is correct but not always.
 

Reply to New panel board required? in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top