New rewire and fuse board - views on work. | Page 9 | on ElectriciansForums

Discuss New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

Debrahim

DIY
Joined
Jan 7, 2023
Messages
49
Reaction score
6
Location
London
Hi,

I’d appreciate views on the fuse board.

It’s been completely rewired and I’m unhappy with the quality.

I’ve messaged him about it and described the board as a complete mess, and poor workmanship ship. For entry for the 25mm cables and 16mm tails he used the knock out but didn’t bother using the plastic cable holder - which is a couple of quid.

Also with the cables coming in through the back, there is no plastic or anything so the metal of the board could rub against the metal of the board.

his reply is below

a. - there is a reason why cables shouldn't be perfectly arrange in the fuse box because it could create electromagnetic field resulting in humming sound in the fuse box- you would probably think that's ridiculous ! But it's a fact!


Quite frankly I’m shocked, would you be happy with the work, paying over 4k? And supplying the board all second fix items etc? So basically 5k?

He has also created 5 additional lighting circuits downstairs, I live in a three bed terraced house.

1) for 6 down lights in a 2.5m x 2m room.
2) just the ground hallway light.
3) the lounge dinner, two lights and two wall lights.
4) a porch light and floodlight.
5) under stairs light simply 2 lights.

His reply is that it is is better… but then it’s all on a dual rcd so it doesn’t really help in my opinion.

We agreed the whole of downstairs on a circuit except the hallway on a separate one. (He said that was best practice.

I’ve attached photos and the pieces that I believe should go there. One is too big.
 

Attachments

  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    524CC7D8-A048-4BC8-90DD-E2F06AE59EFF.jpeg
    505.9 KB · Views: 152
  • [ElectriciansForums.net] New rewire and fuse board - views on work.
    C4DC1E06-3B9A-41F4-9248-9C59CC8D36C1.png
    325.7 KB · Views: 133
Good luck with that for a Hager RCBO. Current price for a domestic Hager RCBO would be over £35 from us.

Also if you are intending to add an EV chargepoint to this then you are ignoring the fact that each EV chargepoint must have its own dedicated RCBO which breaks all live conductors, which a typical UK-style single module Hager RCBO wouldn't achieve.

Out of interest - who is 'us'.

Is this the wrong RCBO ? Hager ADA332G 32a 30ma RCBO - https://www.edwardes.co.uk/products/hager-ada332g-32a-30ma-b-curve-rcbo-type-a-ac-and-pulsating-dc-sensitive-?gclid=CjwKCAiAk--dBhABEiwAchIwkZZ0mEjx0iIVv-zzqWULFu3km1cWGJO27E0qIJujj3vWNowd_8gBGBoCS2gQAvD_BwE

In any event I need to find a decent spark, to go further.
 
Edwardes have keen prices on some items, including some Hager RCBOs.
Around £30 is the top (sensible) price for the same RCBO (e.g. CEF), at least in mainland UK.
Which wouldn't be £30 to the customer though. Didn't realise that Edwards had them at that price. Still nowhere near the £10 claimed though.
 
Is that single pole?

If you are getting RCBO's then I would suggest double pole units which do cost more.

It's frustrating that the data sheet isn't clear on this.
EDIT CEF have a close up of the diagram on the side of it which confirms it is single pole.
 
Last edited:
From the first image posted, the only thing we can say is it’s untidy.

We now know the SPD is correct, taking the earth from the din rail clamp.

We now know it wasn’t a full rewire. The kitchen was already done, so it’s been a lack of communication as to which circuits were rewired. He may have priced the job on so many circuits, then on site found there were extras.

If this board on the picture was to be given an EICR, the worst outcome would be a C3. In which case, there is no requirement to have it redone.
It is not immediately dangerous, nor potentially dangerous.
Visually, the plastic board below is a definite C3, and the one hanging to the side would be C1 if it’s still connected.

Do we know what the job looks like now the board is complete?
 
@westward10 my understanding is that they look like this - and I'd expect to see some glimpse of the CPC .
View attachment 105116


That wasn't the wisest move really.

What did he want to fit? Was it Fusebox? Any RCBO board would have been better.
If you supplied the board how did he end up with exactly the right number of B6 breakers for lighting unless you also knew the plan in advance?

The main reason is that the regs encourage us to design to limit cumulative earth leakage and specifically tell us to consider RCBO's in residential premises. (Section 314 and section 531.3.2 )
I have only fitted 1 Hager SPD board and it was supplied with no earth lead just the galv bar which links the 2 earth terminals and is fixed to the metal case by screws or rivets (can't recall)..It seemed odd to me but there was no further info in the paperwork. Connection to outgoing side of mainswitch was the offset busbar as shown in your post.

* EDIT * Have now read the full thread and find I am just repeating what others have said !!
 
Last edited:
thanks for the comment but i claimed a tenner less - i.e instead of £30 ish, £20ish in some places
Me personally would put that Hager Cu on eBay and replace it with a fusebox spd, d/p rcbo one, combine the circuits from that other CU and have done with it.
 
From the first image posted, the only thing we can say is it’s untidy.

We now know the SPD is correct, taking the earth from the din rail clamp.

We now know it wasn’t a full rewire. The kitchen was already done, so it’s been a lack of communication as to which circuits were rewired. He may have priced the job on so many circuits, then on site found there were extras.

If this board on the picture was to be given an EICR, the worst outcome would be a C3. In which case, there is no requirement to have it redone.
It is not immediately dangerous, nor potentially dangerous.
Visually, the plastic board below is a definite C3, and the one hanging to the side would be C1 if it’s still connected.

Do we know what the job looks like now the board is complete?

I'd tried to bring similar grounding to this thread two days ago, in several comments that culminated in post #86, but that seemed to fall on deaf ears and I decided to step back.

There's nothing to be gained by people urging the OP to act on the basis of anything other than clearly establised fact and a number of comments blur the lines between preference, opinion and what is clearly stipulated in The Wiring Regulations.

It's obvious to everyone that some aspects of the work carried out are far from ideal, but far from ideal doesn't constitute wrong doing and perhaps everyone (OP included) might be better served if such distinction is made clear.
 
I have been advised that a dual RCD board is bad, and that I should have RCBO's - you guys are the experts, if its a matter of safety, i'm happy to swap.

There has been no tripping. I allowed extra space for the solar/car charger, but thought,

Thank you, however the law says that the work must be carried out with skill and care. The test is whether a ‘reasonably competent member of the profession’ would leave it like that.

Everyone here said it’s sloppy and poor. If you boards look like this then I’d be interested to see ?

He didn’t use a torc screwdriver nor did he do any testing. I know as I was there.

The tails inside are just free floating and hanging - no clip to hold them in place, is that legal?

The cables come through the back via the metal, there is no grommet or plastic to protect the cables against the sharp metal edge again is that legal ?

The socket has a massive hole there, my finger could easily fit in there, is that legal ?

The
You have been advised wrong - Installing dual RCD CU is not a problem at all. Currently we are installing the same Hagger CU in luxury apartments complex. If you want to know about what is legal or not, I think you have to consult a lawer. BS7671 is actually not a legal document.
 
You have been advised wrong - Installing dual RCD CU is not a problem at all. Currently we are installing the same Hagger CU in luxury apartments complex. If you want to know about what is legal or not, I think you have to consult a lawer. BS7671 is actually not a legal document.

I'm surprised you aren't using full RCBO boards in high end projects.
 
You have been advised wrong - Installing dual RCD CU is not a problem at all. Currently we are installing the same Hagger CU in luxury apartments complex. If you want to know about what is legal or not, I think you have to consult a lawer. BS7671 is actually not a legal document.
It depends on the situation, dual rcd boards are not really suitable for some installs.
 

Reply to New rewire and fuse board - views on work. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top