New single light circuit tripping RCCB on socket circuit. | on ElectriciansForums

Discuss New single light circuit tripping RCCB on socket circuit. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 20, 2019
Messages
3
Reaction score
2
Location
Fife
I'm not an electrician, but have been successfully doing DIY electrical work for 50 years, including complete house rewiring before the days of RCCBs.

I've just moved to a house built in 2000, and one cupboard (ironically the one with the consumer unit in it) does not have a light. I installed a simple circuit direct from the lighting MCB to a pull cord and a pendant fitting. There is no RCCB covering the lighting circuits. Everything is fine till I switch on the light, then the RCCB for the socket circuits trips. It doesn't trip the MCB. If I use a tungsten bulb, the filament flashes briefly, then goes out, but if I use an LCD bulb, the bulb stays on after the RCCB trips (remember, the RCCB that is tripping only covers the sockets).

I've carefully checked all my wiring, and can't see any problem. I've swapped the bulb holder with another new one, to no effect. The wiring in the ceiling rose clearly looks OK. The pull cord is single pole, and I've connected the earth, and used a strip connector for the neutral. All the cabling is new.

Any ideas, please?
 
Thanks Westward 10, I didn't think it would matter, so just connected to the nearest one. I'll go back and check, and try that.

I'm afraid my experience doesn't include RCCBs, and the only testing equipment I have is an electrician's screwdriver and one of those plugs that checks the wiring of a socket :(.
 
It seems that someone wants to keep this thread operational. I can see the relavence in the fact that the opening poster would benefit from reading up about RCCBs, RCDs, RCBOs and the like to have some appreciation about the level of protection and reasons they are now obligatory in domestic installations.
 

Reply to New single light circuit tripping RCCB on socket circuit. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
358
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
704
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top