It would probably be too tricky to spot from the ground, might be worth looking if there is anything in your design pack. For instance if you had one string of six/seven panels and one of ten/nine, but the string of ten/nine wasn't working then that could explain the current performance.

Well I have easy access to the loft, where the inverter is, and also have a velux window in my roof whith the solar panels built around it, so may be able to look?
 
The inverter should switch between each MPPT or string on its small display screen giving you string voltages. They should be very similar if 8 panels per string, if one string was not working then the string voltages would show this up.
 
If you go to the inverter you will see up/down arrows. Using one of the arrows scroll through until you reach:

Vin1
Iin1

Vin2
Iin2

Please let us know what readings you have. They will be something like Vin1 380V Iin1 1.5A
 
[ElectriciansForums.net] New solar panels poor performance, can't contact solar company! Apolo solar.[ElectriciansForums.net] New solar panels poor performance, can't contact solar company! Apolo solar.[ElectriciansForums.net] New solar panels poor performance, can't contact solar company! Apolo solar.
 
ok input 1 isn't working properly, given your max figure, my suspicion is they haven't set up the dual tracker / parrallel tracking system correctly as IIRC 2.4kW is the peak output from one side by itself.

but I'm a bit confused by the voltage reading on Vin1

it will be simple enough to fix probably, unless there's another issue with string 1 developed as well
 
ok input 1 isn't working properly, given your max figure, my suspicion is they haven't set up the dual tracker / parrallel tracking system correctly as IIRC 2.4kW is the peak output from one side by itself.

but I'm a bit confused by the voltage reading on Vin1

it will be simple enough to fix probably, unless there's another issue with string 1 developed as well

Ok, that sounds slightly reassuring, I only wish I'd have pushed the issue with the fitters soon after getting them fitted!
How would you suggest I would go about getting the problem fixed?

Again, thank you so much for your advice!
 
.. Just to say, the max it had given out (Ppk) is actually 2502W, not 2.4kw as I wrongly said earlier.. Sorry for the wrong number..
 
The 240 (ish) Volts from the functional string suggests 8 x panels operating at an optimum of about 30 Volts (8 x 30 = 240V), so you probably have two strings of eight panels which is not unusual for a full-size 3.8-4kW, 16-panel array.

If your panels are nearly South-facing they will probably produce real-world peak power a bit higher than their nominal value, which probably explains peak readings of 2.4-2.5kW which would be consistent with one string of eight panels operating a bit above their nominal rating of 2kW in perfect conditions (mid-day, late spring/early summer, sunny, cool, breezy, shortly after rainfall has just cooled and cleaned the panels).

As said earlier: it looks like one of the two strings isn't working at all. Basically your 'engine' is only firing on two cylinders.

Probably a very simple fault on the 'dead' string of panels; either not being connected properly or the inverter not set to receive from two strings.
 
142v is not enough for the MPPT to operate, assuming the inverter has been left in its default setting.

The inverter needs 200v before it will start which is why there is zero amps showing. The voltage start up can be lowered, but there appears to be something wrong which i causing the low voltage.

What kind of a layout are the panels in? I wonder whether one of the strings has a couple of panels wired back to front? Possibly due to an incorrectly installed fly cable, perhaps around the velux window?
 
That could explain it ^^^^
Install looks quite tidy though, nice to see cables nicly clipped too, after some of the carp that customers post on here..
 
actually my previous post is not quite right, the limit per tracker is 3kW not 2.4, but there's something odd with the inverter as the 3.6 should have 2 x pairs of inputs on input A, and yours only has 1 pair.
 
142v is not enough for the MPPT to operate, assuming the inverter has been left in its default setting.

The inverter needs 200v before it will start which is why there is zero amps showing. The voltage start up can be lowered, but there appears to be something wrong which i causing the low voltage.

What kind of a layout are the panels in? I wonder whether one of the strings has a couple of panels wired back to front? Possibly due to an incorrectly installed fly cable, perhaps around the velux window?

Please excuse my childlike, not to scale sketch, but this is the layout..[ElectriciansForums.net] New solar panels poor performance, can't contact solar company! Apolo solar.
 

Reply to New solar panels poor performance, can't contact solar company! Apolo solar. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
813

Similar threads

  • Question
I wish I needed a solution to me keep needing get batteries out my 6m boat!
Replies
5
Views
539
Oooo I think you have demonstrated why it doesn't pay in the end to DIY something dealing with power there mate, to be frank! You had any solar...
Replies
1
Views
203

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top