Hello there

I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of warranty!

None of the wiring set up has changed other than a new AC plug for the Solis inverter. I have a 16-panel 4kw system.

It seems, when the inverter 'wakes' in the morning it trips the main house electrics RCD/consumer unit. The solar system is running through a 20amp RCD on the consumer unit and as I say, this is how it was originally installed (and worked well until the Sungrow failure!). I have replaced the RCD just in case that was the issue but it still trips at start-up.

Any suggestions please?

One thing I'm not clear on (install instructions vague?) is: should I run a separate EARTH cable from the AC side isolator switch to the Solis inverter's case? Could not having this be causing the daily trip?

Thanks
 
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
Hi Norton, the middle RCD/main protected circuits keeps tripping at start-up. Hope that helps? Thanks.
 

Attachments

  • IMG_0932.JPG
    IMG_0932.JPG
    429.7 KB · Views: 107
Can you post up a pic of your CU?

Is the solar on a shared RCD board. What is actually tripping? Main RCD?

Thanks

Norton
...the solar has been wired into a spare within the protected circuits area so ends up tripping the house sockets, cooker, shower etc that are on the protected RCD?
 
Some inverters leak a lot to earth and should not be on a 30ma (RCD) Residual Current Device especially a shared one for this reason.
 
Dangerous as well. If an earth fault occurred, such as you making contact with live mains, the RCD should disconnect the power in a sufficiently short time to prevent you from being electrocuted. The RCD will switch off as intended, but power will still be being supplied by the PV array, until it detects the loss of mains power and shuts down as well. This time will be far greater than the time it takes to electrocute you.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
New Solis inverter trips house electrics
Prefix
Solar 
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
iainco,
Last reply from
brianmoooore,
Replies
5
Views
3,437

Advert

Back
Top