I realise that for most modern houses, fusing down to say, 40A, would probably be impossible due to the power requirements at certain times (shower/cooker etc)

The average domestic installation with gas central heating, without electrical shower unit, would rarely see 40A at the meter. My parents house had a 60A cut-out fuse and a 40A meter. They were both changed (80A fuse and 100A meter) in 96, but had never had a problem with either!! ...lol!!!
 
I've seen 1.6:1 and even 2:1 mentioned for fuse discrimination. Based on that you wouldn't achieve discrimination using an 80A fuse with a 100A main fuse, you'll be needing a 63A or even a 50A fuse.
 
Personally, provided the cabling is protected, I would go for the maximum fuse to match the main incomer. Let's face it, how often does the 100A or 60A main fuse actually blow? Why should we restrict the customer's supply potential for the chance at providing the possibility of genuine discrimination on the rare occasion that a fault would take the mains out anyway?
 
so if the DNO fuse blows - change the bugger and no one would know - saying that, had one blow in a ryefield board before, customer phones DNO, they came out within an hour and changed it for free !

not sure if its usually a freebie ?
 
so if the DNO fuse blows - change the bugger and no one would know - saying that, had one blow in a ryefield board before, customer phones DNO, they came out within an hour and changed it for free !

not sure if its usually a freebie ?

Not the wisest post, in that you are suggesting the OP commit an illegal act, might give the wrong impression to any member of the public about what we stand for,.... yes agree! it happens but could have been worded as a play on words.....( If only you were allowed to replace the service head fuse yourself ;) )
 

Reply to New supply tails in trunking or SWA? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Yeah, been unwell but better late than never!
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top