I realise that for most modern houses, fusing down to say, 40A, would probably be impossible due to the power requirements at certain times (shower/cooker etc)

The average domestic installation with gas central heating, without electrical shower unit, would rarely see 40A at the meter. My parents house had a 60A cut-out fuse and a 40A meter. They were both changed (80A fuse and 100A meter) in 96, but had never had a problem with either!! ...lol!!!
 
I've seen 1.6:1 and even 2:1 mentioned for fuse discrimination. Based on that you wouldn't achieve discrimination using an 80A fuse with a 100A main fuse, you'll be needing a 63A or even a 50A fuse.
 
Personally, provided the cabling is protected, I would go for the maximum fuse to match the main incomer. Let's face it, how often does the 100A or 60A main fuse actually blow? Why should we restrict the customer's supply potential for the chance at providing the possibility of genuine discrimination on the rare occasion that a fault would take the mains out anyway?
 
so if the DNO fuse blows - change the bugger and no one would know - saying that, had one blow in a ryefield board before, customer phones DNO, they came out within an hour and changed it for free !

not sure if its usually a freebie ?
 
so if the DNO fuse blows - change the bugger and no one would know - saying that, had one blow in a ryefield board before, customer phones DNO, they came out within an hour and changed it for free !

not sure if its usually a freebie ?

Not the wisest post, in that you are suggesting the OP commit an illegal act, might give the wrong impression to any member of the public about what we stand for,.... yes agree! it happens but could have been worded as a play on words.....( If only you were allowed to replace the service head fuse yourself ;) )
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
New supply tails in trunking or SWA?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
ChevyKevv,
Last reply from
Darkwood,
Replies
22
Views
4,862

Advert

TrueNAS JBOD Storage Server

Back
Top