Dont worry its easily done at the start at least your doing it right not the pub diy bloke way !
 
[ElectriciansForums.net] New to testing... Ze, PSCC & PEFC
 
Because ive read in a number of places that Max Ze is..

TNCS = 0.35
TNS = 0.8
TT = 20

So because TNS is 0.8 as wrote and not 0.80,
This was why im thinking i have to get it lower than 0.8
 

lol cool !

I am new to testing and im trying to learn all i can about each test.

Today i have been practicing my Ze tests, PSCC & PEFC.

Please can someone tell me if i am performing the tests the correct way and if my results look genuine?
(I have a feeling my results on this occasion are way out)

I have added photos.
(If i press the "Display" button on my tester i will also get a current reading. So 2 photos to each test)

My Ze seems very high, Unless im doing the test wrong. Its a TN-S Supply and i understand 0.8 is the maximum.

I appreciate any pointers.

tut tut and wheres your safe isolation ? (switch off and lock off) etc etc ?
 
Last edited by a moderator:
Right, Heres my second go..

This is a TNCS, Better photos..

I know its a peice of cake to most of you but have i sussed it?

I lost my green crock clip, thats why using black one..

(And yes I do like creme eggs!!)
 

Attachments

  • [ElectriciansForums.net] New to testing... Ze, PSCC & PEFC
    My Ze.jpg
    73.9 KB · Views: 282
  • [ElectriciansForums.net] New to testing... Ze, PSCC & PEFC
    My PEFC.jpg
    75.1 KB · Views: 272
  • [ElectriciansForums.net] New to testing... Ze, PSCC & PEFC
    My PSSC.jpg
    77.3 KB · Views: 255
Good Good!

So on EIC..

I put in the "External Earth Fault Loop Impedance Ze" = 0.20
& For my "Prospective Fault Current" from my readings what would you put in the "kA" Box ???
 
Good Good!

So on EIC..

I put in the "External Earth Fault Loop Impedance Ze" = 0.20
& For my "Prospective Fault Current" from my readings what would you put in the "kA" Box ???

Yep and the PFC box you put your highest value of PEFC or PSCC which is 1.01.

Odd though as normally on a TNCS they are near enough the same, but dont worry about that for now!
 
Last edited by a moderator:
So from my readings you'd put in "1 kA"

and the maximum this can be is 16.5kA, Is this correct?... and this will be written in the "Short Circuit Capacity" Box on the EIC?
 
So from my readings you'd put in "1 kA"

and the maximum this can be is 16.5kA, Is this correct?... and this will be written in the "Short Circuit Capacity" Box on the EIC?

Ok Nature of Supply etc.

External EFLI Ze is the max so for TNCS its .35 There is then a box underneath for Measured Ze

PFC Single phase is what you measure so 1.01kA

Short Circuit Capacity is normaly 33kA for BS 1361 Type II 100A fuse.
 
Last edited by a moderator:
Ok thanks J.. I dont know where ive got 16.5 from, ive seen it the max for something.

Where in the red book would i find these figures?
 

Reply to New to testing... Ze, PSCC & PEFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
605
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
949

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
390

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top