Though not a great lover of the OSG there are some good guides in it and one is the 1/8 one (Page 68 Section 7.2.3) , that an unfused spur length off of a ring should not exceed 1/8 of the furthest point of the ring.

The 3 metre ruling would not apply to a RFC simply because

1) Your concerning yourself with the overload side of things, or you should be. The earth fault protection should still be provided by your 32amp protection device provided that the spur would not exceed that Zs value for that device. Which is why the 1/8 rule is pretty good, if you ensure this there is very little chance your spur will fail on Zs

So it is more the over load side your concerned with, that is a single 2.5mm cable being protected by a 32amp PD. Well that is where I agree with you concerning a spur should only connect into a BS 1363 accessory, because these accessories all are limited to 13amps and you therefore conform to reg 433.2.2

This is why I always say to guys who ask can I spur of a ring final into an enclosure and just put 6amp for lighting and a 10amp for socket no. IMO it is a bad design and opening the design up to abuse

Yes in theory you can, that 16amp load will not stress a 2.5mm cable. But even in a domestic situation there could be a chance that you may have a problem with a socket(s), you may have a fridge/freezer on it and a washing machine and it may just trip occasionally when the heating element is on and the fridge starts up, so what happens ,the MCB is increased to perhaps a 16amp or even more.

By designing a spur into a non BS 1363 accessory is opening up that circuit to abuse in the future and IMO bad practice.
 
I do agree Malcolm, totally.
far to many circuits are badly designed now, and do not comply on many levels.
Im sure I was told 3metres max length for a spur on my 2391 course. Maybe a over the top limit.....
Tbh I never really checked.
Personally I would never really have a spur exceeding 3m as i dont see the need.
knowing what people are like... from the one spur they will have two 13amp appliances LOL

I too am not a fan of the OSG maybe why I missed the 1/8 th rule. Will have a look.

Thanks for the reply :)
 

Reply to Newbie question... garage circuit connected to ring final circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top