night tariff meter change to standard tariff | Page 2 | on ElectriciansForums
Discuss night tariff meter change to standard tariff in the The Welcome Forum area at ElectriciansForums.net
What you need to do, is get the DNO to remove the off peak meter and to have ready a dual isolator for them to connect the meter tails into.
Then you can connect both CUs into the dual isolator.
As Westward10 says, you will need to provide RCD protection for the sockets.
Problem here he is missing rcd protection with the existing board, suppose you could fit rcd sockets.
i think it would be easier if i can take the four 2.5mm t&e radial feeds from the economy 7 consumer unit and connect them to the main tariff consumer unit which has split load rcd and install 16 amp mcb for each radial circuit. this should cover all bases.
Yes if there are adequate spare ways.
"537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply."
Just a reference on this.Hello,
Please offer clarification as to whether regulation 537.1.4, or in fact any other regulation prohibits the common practice of splitting the mains supply from the meter, via Henley block to 2 or more CCU's? Each CCU in its own right has DP isolation. Does this regulation, or in fact any other regulation insist on a suitably rated DP isolator to be placed in line with the meter tails offering a single point of isolation for the 2 or more separate CCU's.
Note, an assessment of general characteristics would additionally be conducted to ensure compliance.
This question needs a written answer as evidence to address the questions within my immediate circles, that the above practice of splitting the mains supply via Henley block doesn't comply with the Regs and specifically 537.1.4.
Thank you.
Regards,
NICEIC response:
Wango
Please accept our apologies for the delay in replying to your query.
I can confirm that such practice is allowed under BS 7671. Attention should also be given to 537.2.1.3 & 537.2.2.6
I hope this helps.
Regards
**** ***** BSc MIET IEng
Area Engineer
Reply to night tariff meter change to standard tariff in the The Welcome Forum area at ElectriciansForums.net
Interesting what you say, I have allowed with my system for the change to be half hour out, so start charging at 0:30 and stop at 7:30 but night...