Evening all. I have been asked to quote a landlord for a replacement bathroom light as the old ones bayonet fitting was broken, new pull cord as it was one from 1702 which had finally given up and replace the hallway light fitting as it was hanging off the ceiling.
On inspection there are no CPC's in the lighting circuit, it is sheathed twin 1.5mm with no earth. As I was intending to issue a minor works cert for the work, I said to the client unfortunately I cannot test the circuit with no earth and hence I cannot certify it and have walked away from the job.
I understand I could fit Class II lighting but am I right in saying this is done by risk assessment. My initial quick mental risk assessment was that if a tennant wants to fit a metal light they will regardless of a little sticker on the CU saying there is no earth present and therefore my risk assessment said it was too much of a risk.
I did say to the landlord that they should have it rewired in T+E but as expected they don't want the cost or disruption to something that has "worked fine for years".
What would you do in this situation? Was I right in turning my back on this job?
On inspection there are no CPC's in the lighting circuit, it is sheathed twin 1.5mm with no earth. As I was intending to issue a minor works cert for the work, I said to the client unfortunately I cannot test the circuit with no earth and hence I cannot certify it and have walked away from the job.
I understand I could fit Class II lighting but am I right in saying this is done by risk assessment. My initial quick mental risk assessment was that if a tennant wants to fit a metal light they will regardless of a little sticker on the CU saying there is no earth present and therefore my risk assessment said it was too much of a risk.
I did say to the landlord that they should have it rewired in T+E but as expected they don't want the cost or disruption to something that has "worked fine for years".
What would you do in this situation? Was I right in turning my back on this job?