Obviously things change.
The ESC/NICEIC have taken the view, that if the metal fitting/s is/are existing, then changing the CU will not impair the safety of the installation, and that by providing RCD protection, safety will be improved.
The problem I have, is how this relates to the Regulations.
Whilst you are not required to update an existing installation, if it complied with the Regulations current at the time of design/construction.
I'm not aware that an unearthed exposed-conductive part has ever complied, certainly not within the last 46 years.
As such I would consider such a situation to warrent a code C2 if I were to conduct a Periodic Inspection.
To my mind providing RCD protection in such circumstances would not rectify the non compliance.
It may reduce the danger, so that a code C3 would be applicable, but would not remove it altogether, it would not comply with the current Regulations and would not be considered (to my mind) as an acceptable 'departure'.
This then poses problems when it comes to certification of the work.
Regulation 632.4 requires: "Defects or omissions revealed during inspection and testing of the installation work covered by the Certificate shall be made good before the Certificate is issued".
Whilst there is no requirement for you to upgrade the existing installation (if it complied at the time of design/construction) and it would be acceptable to note the defect/non-compliance under 'comments on the existing installation'.
If the installation of the RCD is intended to rectify the defect/non-compliance, it would fail inital verification, as the measure would not still not comply, and would not be acceptable as a departure becuse it does not afford the same degree of safety as would be achieved by compliance with the Regulations.
Then of course you have the fact, that by allowing such a situation to be rectified by the provision of RCD protection, you are effectively allowing any or all of the fittings and accessories to be changed to class 1.
I wonder what next the ESC/NICEIC will allow.
Cables concealed in walls outside of prescribed zones, as long as they are protected by RCDs?
Perhaps exposed live conductors, as long as they are protected by RCDs?