westward10
Staff member
Admin
Supporter
Done a periodic on this a few weeks ago and back now doing remedial. This notice and the previous Report state there are no cpcs through the lighting.
None of the roses have a cpc connected but there is at the conduit boxes they are mounted on in fact I have checked every light and there is a cpc present throughout, early sixties tinned copper T&E and pvc/pvc singles.
[automerge]1571306718[/automerge]
Here they are.
I rewired the lighting on a 3 bed house in two days last week due to twin cable no Earth. Hard bit of graft but all the switch drops barr one I could pull through. I got through a lot of cable that day and sweated buckets.
Once bitten ......
I might be going out on a limb here, your good work aside, would you be suggesting to your client to consider rewiring, unless they were elderly with not too many years left on this mortal coil?
What makes you think a rewire may be advisable?
It looks like 1960's cabling to me?
And I know where we are going with this, if it tests out ok etc etc. But last time I checked, cable manufactures give their cables a 20 year life span, so we are looking at 50 years plus. When is a good time.
Peeves me that some people will spend mortgages on new kitchens & bathrooms, but won't spend anything on the infrastructure of their properties.
Actually the installation doesn't have a huge amount wrong with it. A new rcbo board was put in by other parties a few years ago to a good standard. Very little has changed since it was put in apart from a new kitchen power circuit. We did suggest it may benefit from a rewire should it become vacant but what is wrong is nearly all put right just a few outside lights to replace which have corroded away. All cpcs now sleeved and connected into the roses one broken batten to replace.
TBH I feel you guys are being a tad harsh, if the cpc's were tucked out of sight behind the ceiling roses, with no connected cpc's at the rose termination, then it's not unreasonable to code it as no cpc's present at the point of termination. Of course the fact that they were present should have been observed, but it's hardly the crime of the century. The fact that there is a sticker clearly stating the circuit numbers suggests this was not a 'drive by' EICR as stated, the inspector had in fact noted a defect......you cant do that from a van parked outside.
TBH I feel you guys are being a tad harsh, if the cpc's were tucked out of sight behind the ceiling roses, with no connected cpc's at the rose termination, then it's not unreasonable to code it as no cpc's present at the point of termination. Of course the fact that they were present should have been observed, but it's hardly the crime of the century. The fact that there is a sticker clearly stating the circuit numbers suggests this was not a 'drive by' EICR, the inspector had in fact noted a defect......you cant do that from a van parked outside.
He noted a defect which was not existent. It was worthwhile redoing all the lighting points as some of the cpc connections were somewhat tenuous so apart from what I can't see it is sound enough. I would say again this was inexperience, they saw no cpc at the roses and thought no earth but I looped to the fixing screws which were clearly 2BA and not wood screws. Tap through the back of the roses indicated metal boxes.
That makes sense. I do get errked when some feel frightened of suggesting the 'R' word on a very old installation, just 'cos it tests out ok. I had to replace a damaged socket on a similar aged property, that had the horrible 'green goo'. It tested out fine, but I advised considering a rewire. Not that I would consider the job meself.
westward10
Staff member
Admin
Supporter
Northamptonshire
United Kingdom
Electrical Engineer (Qualified)
No cpc, really.
westward10,
Midwest,