The Ghost

Hi just thought I'd throw this out here for a bit of light entertainment after the @Marvo thread (phew!)
So brother in law asked me to look at EICR which returned unsatisfactory. I have not looked at the installation to ascertain as to Class 1 or 2 fittings in the premises are installed. The bonding seems ok but is not verified on the water which is strange it got a tick. Or seen the DB so can't comment as yet. But there are a few things that are questionable like time for disconnection and C1 for no cpc. Also the box ticked there are no items adversely affecting electrical safety! Would be fascinating to know how he got the PFC considering Ze is .35 and PFC is 1.8Ka. Wondered what your thoughts are. Can't wait to have a look will post some piccys. Not to worry though he is NICEIC approved contractor
[ElectriciansForums.net] No cpc to lighting circuit, no rcd protection 50 year old wiring
[ElectriciansForums.net] No cpc to lighting circuit, no rcd protection 50 year old wiring
. He/They did not want to remove lamps to test L-N IR again odd.
 
The schedule indicates a 1.0 cpc but the IR and Zs readings are omitted or overwritten as N/A. So I assume the circuits predominantly do not have cpcs even though there is one at the CU?
Hopefully indicates cpc present and correct at CU but cut back at light point :)
 

Reply to No cpc to lighting circuit, no rcd protection 50 year old wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
437
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
706
davesparks
D
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
729

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top