C

cambria

Not come across this before but the installation is labelled PME system but there is no earth connection supplied by the distributor. The earth connections are stuffed inside a loose connector in the fuse box and a 4mm cable connected off the incoming water supply, obviously not allowed anyway. Has anyone come across this situation where no earth connection is supplied by distributor and why they would not have done it ?
 
Not come across this before but the installation is labelled PME systemIs this a proper DNO sticker?

but there is no earth connection supplied by the distributor. Have you done an external earth loop test to see if there is an earth?

The earth connections are stuffed inside a loose connector in the fuse box The DNO cutout?

and a 4mm cable connected off the incoming water supply,Is this a Bonding cable or is it the Earth conductor?

obviously not allowed anyway. Has anyone come across this situation where no earth connection is supplied by distributor and why they would not have done it ?

>>>>>>>>>>>>>>>
 
Yes 'PME system' is printed on the DNOs cutout box
The only earth connedction is the 4mm cable which goes from the loose connector inside the CU underground alongside the incoming water pipe so guess this is an earth not bonding connection.
Earth loop test performed but this is only going to the 4mm cable mentioned above
 
So with it looking like there are no conductors coming from the DNO cut-out and therefore the installation is getting it's "earth" from the water pipe, so unless the water pipe comes under reg 542.2.4, then it can not be used as an electrode.

I would now call the DNO and tell them exactly what you have found, a cut out with a PME sticker on it, that has no obvious PEN/PEL connection and remind them that they have a duty to maintain a TNC-S system, if this is what the system is, either way they should send someone out and it may solve the mystery.

Are you going to fit rod(s) to TT the system.
 
The only earth connedction is the 4mm cable which goes from the loose connector inside the CU underground alongside the incoming water pipe so guess this is an earth not bonding connection

Can you physically see the 4mm connected to the water pipe or could it go to a buried electrode somewhere???

You mention having carried out a loop measurement, what reading did you get and was this with the 4mm conductor disconnected from the 'connector'???
 
Picture would be great

I have a feeling its a modern style PME cutout which get fitted in new build installations, the block is integral with the cutout neutral and you have to knockout a hole on the top and a hole on the front to reveal the allen key termination.
 

Reply to No distributor supplied MET on PME sytem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top