Im sure this has probably been asked before in this forum but ive just upgraded a fuseboard today and found no earth in the lighting (two core). Obviously the next thing to do would be to tell the customer either rewire or change everything on that circuit to class 2 fittings and accessories, but in this case the customer didnt want to go ahead with either.... what should i do? Cutting the circuit out would be abit extreme?
 
All in all I think op you have just been very unfortunate with this customer....I’ve never had one yet that when the dangers of no cpc were explained didn’t opt for class 2 fittings...
 
Last edited:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
No earth in lighting circuit what next?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
228
Unsolved
--

Advert

Thread statistics

Created
Elliott96,
Last reply from
dksanders,
Replies
228
Views
69,413

Advert

TrueNAS JBOD Storage Server

Back
Top