Im sure this has probably been asked before in this forum but ive just upgraded a fuseboard today and found no earth in the lighting (two core). Obviously the next thing to do would be to tell the customer either rewire or change everything on that circuit to class 2 fittings and accessories, but in this case the customer didnt want to go ahead with either.... what should i do? Cutting the circuit out would be abit extreme?
 
All in all I think op you have just been very unfortunate with this customer....I’ve never had one yet that when the dangers of no cpc were explained didn’t opt for class 2 fittings...
 
Last edited: