I would go back immediately and disconnect your made up tnc-s system. Revert it to a TT system with a newly fitted earth spike and cover the installation with a 61008 device as you cannot just go around making up combined neutral and earth systems.
BillR3
 
if it wass tt and you were getting an eath path through the water,strucural steel ect you would get 230v try it agian one all main bonding has been disconnected i would be suprise if there was an eath.
Call supply authority see what system they have installed if they say tn-c-s thenits ther responsibility to provide an suitable earth terminal.
 
I would not convert to a TNCS. It sounds like it is a TT with the earth spike just not visible. If anything convert to a TT. As said before due to the construction of TNCS (PME) the dno is the one who does the change, it is (should no be) a simple connection in the domestic premisis.

A quick check of the incomming cable in the fuse block will tell you if it is TT or TNS or TNCS. TT generally will not have 'armour' and will have 2 cores, TNS will have steel armour or lead sheath and 2 cores, TNCS will have a single core with the 'armour' being half copper and half steel.
 

Reply to No earth loop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top