Hello,

Just a quick q....

Went to change a cu and carried out a few test and visual inspections. Found a problam, I think the cable was micc but couldn't tell as none of ends were made off. All cables for all circuits where 2 core NO earth. Zs test on sockets came out with >99kohms....

No I am have a argument with another spark... I think there is no point in installing a rcd cu yet as it wouldn't make any differnce...

What do u all think?
 
you are wrong !!
how is that wrong obviously a earth would always be better but a rcd only measures any imbalance between live and neutral and if you touch something you shouldn't there will be a imbalance between live and neutral as what is going through you will not be be returned and the rcd will notice the imbalance and operate, you dont connect a earth to a rcd
 
I would say that the whole of the install would be worthy of a thorough inspection and test before any proposed works proceed as you will just end up inheriting the existing problems. If the MICC has not been correctly terminated then chances are that the magnesiun oxide within the cable could be damp as it is hygroscopic
 
you are wrong !!

I fixed a problemm recently on a circuit without an earth and the "broken" cable was tripping the RCD

Back to the OP, wouldn't an urgent thorough inspection be required?? I certainly wouldn't touch this install without this first, and probably remedial workk before considering the CU.
 
I would say that the whole of the install would be worthy of a thorough inspection and test before any proposed works proceed as you will just end up inheriting the existing problems. If the MICC has not been correctly terminated then chances are that the magnesiun oxide within the cable could be damp as it is hygroscopic
i agree. by the way, it's hydroscopic
 
If the MICC has not been correctly terminated then chances are that the magnesiun oxide within the cable could be damp as it is hygroscopic


If MICC, this wouldn't cause the loss of earthing etc, but would cause far bigger problems to this installation!! lol!!
 

Reply to No earth... Zs and rcd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
969
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
398
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
699
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top