No earthing on lighting circuit | Page 2 | on ElectriciansForums

Discuss No earthing on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

KevinH

-
Joined
Apr 28, 2018
Messages
75
Reaction score
86
Location
Pembrokeshire
Hi all, I've been asked to make an old 4 story townhouse "safe" and issue cert for renting out.
Hasn't been touched for so long it has bakerlite accessories with wood backing!
Straight away I'm seeing replace all accessories, replace CU, upgrade earthing. The wiring is all in PVC cables but typical no earthing on lighting circuits.
I hear you all scream "REWIRE"!
Problem is property is highly decorated and furnished and owners would rather not go down that route.
My question is, if I fit all plastic accessories throughout, and clearly state on CU and cert NOT to fit any metallic fittings. Can I get away with that?
Just asking as whenever I've come across this problem in past, I've always rewired lighting so bit unsure what complies.
By the way, I've done quick IR, ring loop tests, Ze etc and all ok, but how do you R1+R2 lighting with no earth?
 
Not sure what the relevance is unless the op was suggesting a re-wire with no cpc.

I'll be honest, I'm not entirely sure of the relevance either, but I took it to suggest that the method of using class 2 accessories, mentioned in the same section, should not be employed in a domestic situation. Otherwise what would be the point of putting it in the guide to consumer unit changes ?

If we are to ascertain that all existing equipment is safe for the alteration before work commences (132.6),
and if 412.1.3 deems that the method of double insulation is not to employed in a domestic situation, then we cannot fulfil our obligation to the requirements of 132.16 if it is employed.
 
Interesting points from both sides of the argument but I can’t see how you can class something as potentially dangerous if plastic accessories are fitted throughout the lighting circuit(s).
On the other hand an unearthed back box tho not necessarily accessible to touch could become live through breakdown of the insulation and if the homeowner was to decorate the wall then the added influence of water could have dire consequences.
Yet as stated there’s no law to say an installation must be upgraded to current standards.
The obvious problems start when we alter the circuit and installation and we need to comply with 132.16.
What I do know is, it does seem to be an acceptable practice in the industry to label the DB and have only plastic accessories throughout the circuit
Think I need a lie down
o_O
 
Indeed such an approach is not actually recognised by BS7671 - I bet no-one can find the wording of any such label within any Edition of the Wiring Regulations.
There’s a requirement to provide labelling at the DB for circuits with high protective conductor currents but no such label exists in bs7671 so it’s a similar situation label wise I mean.
The label for protective currents above 10mA is required by bs7671 in section 543 and is mentioned so perhaps that is indeed the big difference between the 2.
Often labels required are not actually in the wiring regulations themselves.
 
There’s a requirement to provide labelling at the DB for circuits with high protective conductor currents but no such label exists in bs7671 so it’s a similar situation label wise I mean.
The label for protective currents above 10mA is required by bs7671 in section 543 and is mentioned so perhaps that is indeed the big difference between the 2.
Often labels required are not actually in the wiring regulations themselves.
OK, but the fact remains that not having a cpc terminated at every point in the wiring is not permitted by BS7671 for an ADS system.
 
What you should do is provide RCD protection along with plastic accessories and the label.

Agreed, I was going to raise that. Given the suspected age of the installation I would suspect that there is no RCD protection. I would want that, for a rented property, on the sockets at least.
 
Agreed, I was going to raise that. Given the suspected age of the installation I would suspect that there is no RCD protection. I would want that, for a rented property, on the sockets at least.

It shouldn't really make a difference as far as RCD protection if the person has bought or is renting the house. But I know what you mean.
 
Thanks for all your helpful advice.
Just to clarify to the last few posts regarding RCD protection, I was planning on replacing the CU and ALL circuits would have RCD protection.
I would not be altering any cables in any circuits, just replacing accessories.
Also, I planned to replace all switches with plastic ones and use the push in plastic screw covers usually supplied with them, also all switches would be mounted on plastic surface backboxes to maintain the best insulation I can.
On a similar note, i'm surprised that they don't make labels to mount on/near the CU to warn of no earthing on lighting circuits, as i'm sure this is a common issue in very old properties. I'm assuming its just a case of getting the labelling machine out and typing something to that effect.
 
I stand corrected on my last post, turns out they do make "no provision for earth" labels. I just ordered some. I should have checked before sending post, oops.

[ElectriciansForums.net] No earthing on lighting circuit
 

Reply to No earthing on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
671
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
363

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top