I've been asked by a client to fit 10 NO Emergency stops points in a training facility. My question is has anyone fitted these before (I'm guessing the answer is yes) why would a switch like this be used for emergency stop?

he request is also to fit 10 NO fused spurs too.

Am I being naive here or has it just been too long of a week.... Please help!
 
As it has been brought up it does seem rereading it that the NO is probably 'Number Of' but the lack of punctuation ie No. or N/O made the post very ambiguous, this could be a mistake by the OP or simply that he has passed on the info' as given, either way I think it matters not to the end advice given.

I would also be implementing RCD cover for said circuits too in addition to my previous postings, this may not be required under the BS7671 depending on install methods but a risk assessment would probably implement them into the design as I assume they are training to wire up smart meters and energising them, probably a very expensive 4hrs of training for a crap wage.
 
this is the email I received.

I have had a chance to speak to my Operations Director and found a list of the work that needs doing in the training room.


Please see below quoted work:


Test Bay Work to be carried out under mezzanine floor.

  • All other existing power to be altered or removed and made safe.
  • TEST BAY to supply and install 2 dado trunking to house 10 no emergency stop points.
  • 10 no switch fused spurs.
  • 1 no emergency lock off with key lock to control the whole room (near the entrance)
  • Boiler switch spur to be swapped to an unswitched spur.
  • To supply and install A/M 3 consumer unit to power all new installs (This will be fed from DB1)
 
So no active safety control monitoring circuit mentioned by the looks of it, totally relying on a very basic arrangement that probably falls far short of requirements, who is requesting this and what knowledge do they have of the relevant safety requirements?

I would be asking them who designed this installation you are been asked to quote and what relevant guidelines/regs it follows as you have your concerns about the design. Tell them you will be happy to quote said work if someone else signs of the design of the safety system.
 
why did the donkey who prepared that request not say 10 x switched fused spurs ( or switched fused connection units). clearasdaythen.
Probably picked up the "switched fused spur" without having the faintest idea what it is and thought he would drop the phrase in a specification, Smartarse.
 
I can't remember the last time NO contact were used for an Emergency Stop. We use 'one NO and one NC contact' on lots of functions, so to monitor it correctly.

Test Bay Work to be carried out under mezzanine floor.

  • All other existing power to be altered or removed and made safe.
  • TEST BAY to supply and install 2 dado trunking to house 10 no emergency stop points.
  • 10 no switch fused spurs.
  • 1 no emergency lock off with key lock to control the whole room (near the entrance)
  • Boiler switch spur to be swapped to an unswitched spur.
  • To supply and install A/M 3 consumer unit to power all new installs (This will be fed from DB1)
Correct me if I'm wrong but isn't this just power for a 'training room'?
Does the guy mean "Isolation points" rather than "Emergency Stops"?
 
Why, do panels often use normally open switched fused Spurs?

You missed my previous post suggesting NO was probably relating to 'number', also of it did indeed mean normally open then it would suggest that the spurs have no power until the tutor uses his key, N/O will not mean the actual spurs are normally open due to the fact you cannot get such a thing, if a spur has a switch on then it cannot be called N/O or N/C.
 
@Spoon
This is a training room and students will be dealing with wiring and energising smart meters, there will be a requirement for the students safety so it will mean E-stop but an E-stop is only as good as the method it is wired in and a full risk assessment should be carried out to ensure it is fail safe and fully under the control of a responsible person (tutor in this case), wiring a very basic system that is not self monitoring would not be suitable in my opinion especially if they intend to just run the live wire through all the stops first and then to the spurs... this is how I read their request.
 
Last edited:
... if they intend to just run the live wire through all the stops first and then to the spurs... this is how I read their request.

Is this the intention OP? I don't like it if it is.
Wouldn't it be better to have a contact that switches the power for the whole room and the 11 E-Stops are wired to this, via a safety relay.
Then if one of the students see someone else in trouble they can hit their E-Stop and that will cut the power, rather than someone running over to whoever is in trouble and hitting their E-Stop.
 
You misinterpreted my post @Spoon I meant through all the E-stops first before then going to each spur, that way any E-stop is in series with all the spurs thus cuts power.

Yes I did misinterpret your post mate. Soz.
 
I would say that this is a description of an emergency switching system as described by BS 4163 which relates to teaching and training areas, and is described in the title as a Code of Practice.
I would therefore suggest that the system should comply with this standard as it would be the minimum level of functionality expected.
If you really are going down the emergency stop route then you must comply with BS EN ISO 13850, and BS EN ISO 13849-1 & -2 for the design and validation if they are to be recognised as emergency stops as ISO 13850 is the international standard for e-stops.
This will require an ISO 13849 Plr of PLc as a minimum.
 

Reply to NO Emergency stop points in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
We have stuck white label tape over super bright charging LEDs before, it blocks the bright glare of the extreme brightness LEDs to stop it...
Replies
11
Views
1K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
546
I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
292
  • Question
Might be 100% genuine and was all caught up etc .Its a very hard game to work out. Thats why many dont even start to play it. Its payment upfront...
2
Replies
33
Views
3K
  • Question
Maybe the track itself is live, are they metal units, I'd be getting it tested properly
Replies
10
Views
730

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks