As title.

Doing an EICR, have come across a couple of DBs, where the neutral goes straight onto the bar on Single phase boards.
Whats your views on this guys?
Should it have a requirement to be isolated? Is there a reg for? If so then it can be coded.
My boss thinks its dangerous. I don't, but I'm happy to have a school day.
The boards have stickers on them, stating supply must be isolated elsewhere before taking cover off as well.
Thanks
 
Only required on TT earthing arrangements.
 
If ordinary persons are using the equipment which equates to households then the main switch must isolate all poles.
The job is a commercial one.
[automerge]1599567757[/automerge]
There is also an argument that the DB should be isolated elsewhere before removing cover. As we know its illegal to work on live equipment.
Also there are a lot of OPDs that are single pole.
 
Last edited:
Is this Is 230v DB,so main switch should isolate both L & N
It is 230V, but on a commercial install. My understanding is that double is essential on dwellings, to protect Joe public. As its commercial then Joe public will never be working on the system. Only qualified or competent personnel.
 
If ordinary persons are using the equipment which equates to households then the main switch must isolate all poles.
Just thinking...what about domestic 3 phase boards? 4 pole isolators?
I suppose it depends on the situation.

Just as an aside....I wonder if Part Peees have been issued for work on some of them big houses (Buckingham and Windsor, for instance).
I'll bet the NIC say they should.

Or Houses of Parliament......plenty sleep in there and call it 'home'.
 
I have a Hager 3-phase Invicta in my house with only a 3-P isolator switch - ie the neutral is not switched on the board. I was told that the 4-pole disconnector next to and between this dis-board and the meter is sufficient. Would you agree?
 
I have a Hager 3-phase Invicta in my house with only a 3-P isolator switch - ie the neutral is not switched on the board. I was told that the 4-pole disconnector next to and between this dis-board and the meter is sufficient. Would you agree?
As long as the 4 pole switches the 3 phases AND the neutral, then, yes, it’s sufficient. That is the main isolation, not the 3p on the board.
 

Reply to No isolation of Neutral in Single phase boards in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

I really can't see a problem with it assuming there is a neutral there.
Replies
6
Views
621
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
746

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top