No lights in two upstairs room | Page 2 | on ElectriciansForums
Discuss No lights in two upstairs room in the Lighting Forum area at ElectriciansForums.net
That’s going to be my next step,dead testing. Just puzzled as to why I detect both wires at switch as live when not connected to switch
There is likely to be a broken neutral somewhere in the circuit.
So obviously with any load connected in the circuit the neutral conductor downstream of the break will be at line voltage as it is connected to the line conductor via the load.
This is assuming you have confirmed this is not a phantom voltage you have measured?
Reply to No lights in two upstairs room in the Lighting Forum area at ElectriciansForums.net
Power off ! The switch wires will be the ones that go low resistance when the switch is turned on and go open circuit when its off.
Depending on the location of the 2 CU's and the quality of materials I'd say £10K-12K. If they're potential tyre kickers don't waste loads of time...
    • Informative