I think you will have a hard time proving whether the gas is extraneous or not .

Disconnect the 6mm bonding conductors from the MET and wander lead test them to the pipework , this will hopefully prove they are connected . C3 for inaccessible connections (Bloody kitchen fitters!)
 
I must say in the relatively short time (2-3 years) I have been undertaking electrical work I am surprised at the amount of times I have come across main bonding which has either been completely removed or made inaccessible. I can't work out if this is due to a lack of understanding on the part of the builder/plumber/kitchen fitter or that they don't care. Either way its a bit worrying!

The builder I work with is a very experienced builder, his standard of work is high and I have known him long enough to know he is honest. However, he had disconnected the main bonding on a recent job and was under the impression that it could just be removed nowadays if there was an RCD.:eek:
 
I must say in the relatively short time (2-3 years) I have been undertaking electrical work I am surprised at the amount of times I have come across main bonding which has either been completely removed or made inaccessible. I can't work out if this is due to a lack of understanding on the part of the builder/plumber/kitchen fitter or that they don't care. Either way its a bit worrying!

The builder I work with is a very experienced builder, his standard of work is high and I have known him long enough to know he is honest. However, he had disconnected the main bonding on a recent job and was under the impression that it could just be removed nowadays if there was an RCD.:eek:

Most of that is listening to the 'crack' in the wholesalers .
It's gospel of course.
 
I come across pipes not bonded all the time. Plumbers and builders seem to take great pleasure in cutting away our earth wires. It's a never ending battle with me trying to explain to a customer I have to bond their main incomers while they tell me it's been fine for the 30 years they have stayed in the property.
Every week I come across. It almost makes a mockery of why we have to do it when you consider how many properties don't have it, or have lost it .
 
It's always the plumbers who get their knickers in a twist about the gas pipe being bonded in the meter box, yet they will go looking for every single other bonding clamp to cut it off of the pipes.


Sent from my iPad using Tapatalk
 
It's always the plumbers who get their knickers in a twist about the gas pipe being bonded in the meter box, yet they will go looking for every single other bonding clamp to cut it off of the pipes.


Sent from my iPad using Tapatalk
Talking about plumbers cutting things off I went to a job the other day where the plumber cut the wiring centre out as he said it was in the way for his pipe work...he made sure he cut them as close as possible to the floor though as well. Other side of cupboard had a clear wall that he could of run up but that would of been too easy. I walked in see what he had done so I asked if he had been smoking crack....rang his boss who I was doing the job for and explained the simple connection of the new boiler and unvented upgrade had now turned into basically a full S-plan and would be costing ÂŁ--- more now due to his muppet plumber. He wasn't happy to say the least.
 
Last edited:
Without reference to any particular post, if a particular piece of pipe work is revealed not to be extraneous it therefore does not fulfill the requirements to be bonded by reg 411.3.1.1.

However, reg 528.3.4 would then need to be considered, for example if the internal pipe work is metal, then that would need to be bonded or effectively connected to the protective equipotential bonding.

Or have I interpreted that incorrectly.
 

Reply to No main bonding seen but good continuity. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
668
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top