Hi, im only just recently qualified and have come across a situation I have never experienced yet, in a block of flats in the hall are the meters that then go off to a switch then cables run into the house, there is no main earth in the house!! the tails are about 10 - 16mm cant remember now sorry. so I was wondering who has to run the earth in and if its me what size earth 10mm ? just want to clarify and what tests do I do and results should I get to be able to pme the system ? thankyou
 
they don't wanna know there saying its the lectrics mans responsibility but isn't there tests you can do ?
 
What are you actually saying is there no earth from the meter position into the house?
if so this is the responsibility of the sparky

If there is no main earth provided by the DNO first enquiry is required to find out if they could provide one. If not then you will need to provide a earth rod and make the installation a TT system

A picture of the intake and meters would be good to try and work out what's happening
 
?? You cant just PME a system this is not your area to mess with.

Ring the DNO and ask if PME is available in that area.

Hi, im only just recently qualified and have come across a situation I have never experienced yet, in a block of flats in the hall are the meters that then go off to a switch then cables run into the house, there is no main earth in the house!! the tails are about 10 - 16mm cant remember now sorry. so I was wondering who has to run the earth in and if its me what size earth 10mm ? just want to clarify and what tests do I do and results should I get to be able to pme the system ? thankyou
 
yea its all run in conduit and by the meter there is no visible earth so I was planning on doing some cals which I cant remember so was hoping someone could inform me if I can pme it, and just run the earth round the building, i will try get pictures sorry I know im crap at explaining stuff
 
I thought you was referring to sub mains to flats? You describe things like my MRS :001_icon16:

It's a bit ambiguous I guess that's what he's refuring to needs some clarification. Seems strange that the exsisting sub main doesn't have a earth from the meter position into the house consumer unit
 
yea its all run in conduit and by the meter there is no visible earth so I was planning on doing some cals which I cant remember so was hoping someone could inform me if I can pme it, and just run the earth round the building, i will try get pictures sorry I know im crap at explaining stuff

What is all run in conduit and is this conduit metal?
 
I can't make out head nor tail of what the OP'S actually on about, he can't seem to answer simple questions on his query either!! I'll wait in anticipation of any photo's that are forthcoming before making any comment...

What is disturbing me, is that he doesn't seem to see any danger or consequence to making his own N-E connection. So let me tell YOU now, in no uncertain terms ''NO'' you CAN'T bloody well PME the supply just to suit your needs!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No Main Earth Help
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
39

Thread Tags

Advert

Thread statistics

Created
sparkie710,
Last reply from
Marvo,
Replies
39
Views
4,385

Advert

Back
Top