martinsayer81

hi guys

just wondering what the process is when my only means of earth is the metal gas pipe!! i have a TN-S system, the main earth is bolted to a metal box that houses the incoming live and neutral, but i cant get a ze reading from it, its only when i connect to my bonding conducter that i can get a ze of 0.27Ohms.

do i call my electricity supplier (southern electric)? will they come and rectify the fault or tell me to fit an earth electrode? if they come out, would it cost me - as its the distributers supply that is at fault, should it be their responsibility?

hope that all made sense!! lol
 
To do a Ze correctly you have to disconnect the Earthing conductor from the MET and test between the incoming Line and EC this is because of parallel paths, but you are saying you have no Earthing condutor at the MET?
 
It is not a TN-S system if there is no earth at all. Sounds more like an old TT with the pipe as your earthing. As tel says, speak to the DNO, as at the very least the head should be upgraded. They are not obliged to give you an earth if one doesn't exist, and may well tell you to install an electrode, but more than likely they will change it to PME for you FOC.
 
Suggest ring DNO report old equiptment that needs to be upgraded, inform them that you also cant get a earth path reading on there earth,

inform customer your installing a earth rod for safety reasons.

hopefully DNO change head and install TNS or PME connection for you
 

Reply to no main earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top