Hi Folks, so doing some testing on an installation today and when i carried out the PFC test i was getting a reading of 11A? I tested and retested and kept getting the same result! So, the installation in question is a shed that has had a split load board installed (by someone else) which is feeding several circuits. this is turn is fed from a DB in the house. the DB in the house main earth seems to be a pipe and the guys who did the install said this needed to be rectified and they were going to contact the supplier about it. So they provided a temp earth in the form of an earth rod. earth fault loop test at db = 21.7 Ohms. Im getting earth fault loop tests for all my circuits come back fine, just this PFC coming back at 11A? any ideas? re-checked my tester on my board at home and got a perfectly good reading....any ideas?
 
11A would seem fine by calculation for the PEFC that you have tested. The PFC that would be noted on the paperwork would be the highest reading between the PEFC and the PSCC. What you need to do in this scenario is do the test between L & N and record the result for PFC.
 
I think we might all be wrong as defined in the BGB
Ipf = prospective fault current
Isc = short circuit current

BYB has deleted the Isc although this is in connection with 712.433 and refers to DC overload I think.
However, there maybe an error as the acronym 'Isc' no longer exists but a few pages back the definition does
 
I'm blaming the Hobgoblin gold for being so easy drinking. And the Sneck lifter, and the Ruby mild, and the Guinness, and the assorted pale ales and bitters.
it's the guiness that's done you. PIRA have got sneaky now that violence has been eliminated.
 

Reply to no PFC in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
842
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top