no rcd present on any circuits. doing a periodic. should i advise this is code 1 cos this is how it should be or code4 cos it was right at time of install? please help
No RCD protection to socket outlets, I would attribute a code 2, cables buried in walls etc etc a code 4.
Our NIC inspector told us any code 2 would mean an unsatisfactory,and as RCD protection to all socket outlets is a recent requirement I would be uncomfortable giving an unsatisfactory to an installation wired less than 5 years ago ,where only the ground floor sockets were RCD protected. Previous to 2008 it was only necessary to RCD sockets which may be reasonably expected to supply equipment outdoors.
Best go to the Electrical Safety Council Website and read/download the guidance notes.how would you code a HMO with no RCD at all and with electric showers to each of 4 flats. regards
True, but for some reason the question has been put at the end of the thread rather than starting a new thread!
But to answer the question, its probably a minimum of code 3 and potentially code 2 ..... all is revealed in the guidance given in the electrical safety first publication (as was ESC!)