No RCD protection for socket outlets rated 32A or greater | on ElectriciansForums

Discuss No RCD protection for socket outlets rated 32A or greater in the Australia area at ElectriciansForums.net

spud1

-
Arms
Joined
Oct 23, 2010
Messages
354
Reaction score
54
Location
Somerset
Hi Guys,

Can somebody shed any light on why socket outlets rated at 32Amps or greater do not require RCD protection under BS7671?

Presumably theres some maths behind it?

And presumably the only exception is in a TT earthing System?

Cheers chaps
 
It's all to do with reg 411.3.x which is about as clear as mud. It's one of those regulations that gives specific guidance for a particular application (sockets less than 32A) without being clear about how to go about installing anything other than that. Suggest you try posing your query in the IET forums - you may get a full answer from the bods on there (or you may not :D)
 
411.3.3
In AC systems, additional protection by means of an RCD in accordance with Regulation 415.1 shall be provided for:
(i) socket outlets with a rated current not exceeding 20A ......
(ii) mobile equipment with a current rating not exceeding 32A for use outdoors

though quite what kind of mobile equipment exists that is rated at over 32A is beyond me
 

Reply to No RCD protection for socket outlets rated 32A or greater in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back