True,but on a TN system with a type C/D mcb it may be that the measured Zs slightly exceeds the max allowed for the mcb....is it worth changing the mcb for a type b when the required disconnection time is met by an RCD?....not for me,there may be reasons why a type b might not be suitable..(high inrush currents etc)....if you refuse to accept that the rcd can provide fault protection ,the alternative is rewiring with a larger cable.....pointless for a circuit which already complies with the regs.