.........no thats not strictly true, TT yes, TN no, the rcd is not to be relied on its is supplementary protection in TN systems only, the values for EFLI must be adhered to really and if you said the maximum EFLI was 1667 when a RCD is used in an exam it would definantly be wrong, EFLI should always be met in TN systems, otherwise why do we need to worry about testing lets stick a RCD on and be done with it.That would depend on other readings.Clearly on a TN system a low ze would be expected,and on a correctly installed final circuit a low r1r2 would be expected,add those together and you should get a low anticipated zs..if you then got a measured zs of 1667 ohms clearly something is wrong. Where the 1667 figure comes in useful is when an existing circuit is found to have a zs reading which exceeds the max permitted zs for the overcurrent device by a fraction of an ohm,but is otherwise satisfactory...the RCd will cover it.
the reason the Megger 1552 gives in most cases a higher than expected result on "no trip setting" is that it uses 15mA and not 25A..Well in that case it does not work and is not fit for the purpose