G

graham123

Doing a periodic at a primary school and am unable to locate where the mains water is isolated from, the earth bar doesnt account for a bond to the water as ive found where all the other go. Ive been told in the past no bond is a 1, but in this case i cant find where it is isolated so a 2 or 3? opinions welcomed
 
If you can't find the connection for the water bonding then do a continuity test from MET to the furthest part of the water system to see if there is bonding in place. If there is apparently bonding in place then it is 3 requires further investigation (though really this should be found at the time). If there is no indication of bonding in place then this would I think be a 2 as there is the potential for danger in the case of a fault.
 
If you can't find the connection for the water bonding then do a continuity test from MET to the furthest part of the water system to see if there is bonding in place. If there is apparently bonding in place then it is 3 requires further investigation (though really this should be found at the time). If there is no indication of bonding in place then this would I think be a 2 as there is the potential for danger in the case of a fault.

'Fraid I dont entirely agree with the test method. It is not the furthest point of the water system that requires bonding,it is the nearest. Parallel paths through conductive parts in contact with the water system will give false results. And it is because the system may be at the potential of the general mass of earth that it needs bonding at the point of entry....if it is at earth potential...you are liable to get a misleading continuity reading to the MET whether it is bonded or not.
The point of entry needs to be found,from there you can establish whether or not the water is an extraneous conductive part. If it cant be located you should assume it is not bonded and apply a code 2,as Richard states...perhaps with an explanation such as. "Unable to locate incoming water supply and associated main bonding,requires improvement"
 
Last edited by a moderator:
'Fraid I dont entirely agree with the test method. It is not the furthest point of the water system that requires bonding,it is the nearest. Parallel paths through conductive parts in contact with the water system will give false results. And it is because the system may be at the potential of the general mass of earth that it needs bonding at the point of entry....if it is at earth potential...you are liable to get a misleading continuity reading to the MET whether it is bonded or not.
The point of entry needs to be found,from there you can establish whether or not the water is an extraneous conductive part. If it cant be located you should assume it is not bonded and apply a code 2,as Richard states...perhaps with an explanation such as. "Unable to locate incoming water supply and associated main bonding,requires improvement"

Yes, this is a better description, I was probably being a little simplistic.
If the point of entry cannot be found then it is not possible to determine correctly if the water is bonded so a code is required of some sort.

I was working on the principle that if you have a continuity check of say 0.01 ohm at a distant part of the water pipework then the consideration may be that the water pipework is in effect bonded (though possibly not correctly bonded, as evidenced by the lack of the conductor at the MET) and would be unlikely to cause a danger in case of a fault so a code 3 may be appropriate.
If you get say 4 ohm then this is not effectively bonded and would need a code 2.

However this "method" is not an approved or regulated means of determining correct bonding and as you say could well be a misleading reading.
Explanations on the form are always good (wish I had thought to put that!)
 
i have to agrre with you richard i have been unable to find the water bonding i then test here and there and if i get a good reading i'd code it as a 3
 
I would not put this as a code 3.
If you cannot find the connection, but believe there is one, then it must be inaccessible, which could be either code 2 or 4 depending upon how dangerous you believe having an inaccessible connection is. It would warrent being recorded as a LIM in any event, as there should be no other reason for you to be unable to find the connection.
 
On any report with my name signed, if I can't be sure of a bonding connection including sight of an appropriate clamp etc. then it's a code 2.

Why would you allow any discrepancy or ambiguity in your report?

There is no advantage to you as the inspector in recording this as a code 3 or 4.
 
how are you iQ..??

plastic pipe?

we doing kitchen rewire at moment, and i aint seen any bonding in this house at all.. they do have 300mA power breaker installed before old 3036 board...

im working myaelf up there in morning, im going to have search...
 
Zs is determined as compliant if the nominal voltage over the current causing disconnection in the required time is greater than the measured/ calculated value of Zs. i.e. Zs * Ia <= Uo

so 1.24 x 100A= 124v so my 230v to earth is more so will comply..???
 
how are you iQ..??

plastic pipe?

we doing kitchen rewire at moment, and i aint seen any bonding in this house at all.. they do have 300mA power breaker installed before old 3036 board...

im working myaelf up there in morning, im going to have search...


I'm fine thanks lol, how are you? Lol!
You mention plastic pipes but they aren't extraneous-conductive parts.

The adequacy of existing bonding should be checked before any additions or alterations to the installation.
 

Reply to no water bond, code query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
919

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
607
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top