Zs is determined as compliant if the nominal voltage over the current causing disconnection in the required time is greater than the measured/ calculated value of Zs. i.e. Zs * Ia <= Uo

so 1.24 x 100A= 124v so my 230v to earth is more so will comply..???

You need the current multipliers of the protective devices for the equation eg:

Type B = X5
Type C = X10
Type D = X20

So max Zs for a B 32 = 230/32X5 = 1.44 Ohms
 
i understand that part but how do you know a circuit will comply with a similar summ.. maybe ive picked up wrong what other guy was telling me.. tea?
You need the current multipliers of the protective devices for the equation eg:

Type B = X5
Type C = X10
Type D = X20

So max Zs for a B 32 = 230/32X5 = 1.44 Ohms
 
i understand that part but how do you know a circuit will comply with a similar summ.. maybe ive picked up wrong what other guy was telling me.. tea?

Because you compare the result of the sum (maximum Zs for the device) with the measured or calculated value of Zs for the circuit.

We use a factor of 0.8 on the maximum Zs figure from the sum to allow for increased conductor operating temperatures under load.

So in the example that I did, you'd take your Zs measurement or calculated value for the circuit and compare it with the value from the sum X 0.8.

As long as your measured/calculated value for the circuit is equal or less than that figure then the circuit is deemed to comply for ADS purposes.
 
comprende!! any other tricks up you sleave.. what about this one hope we havent been here before and you getting sore head.. adding of 1.24 for temperature for volt drop and what other cases..??
 

Reply to no water bond, code query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
605
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top