Zs is determined as compliant if the nominal voltage over the current causing disconnection in the required time is greater than the measured/ calculated value of Zs. i.e. Zs * Ia <= Uo
so 1.24 x 100A= 124v so my 230v to earth is more so will comply..???
You need the current multipliers of the protective devices for the equation eg:
Type B = X5
Type C = X10
Type D = X20
So max Zs for a B 32 = 230/32X5 = 1.44 Ohms