Testing Ze (TNs) prior to fitting a small 2 way unit for a kitchen....disconnected main earth and my tester is flashing telling me polarity is wrong ( it’s not polarity as I can confirm that visually) so I reconnect the main earth and test straight to the external MET and get a reading.....so obviously parallel path giving me a reading, out of curiosity I also clamped sheath of DNO incoming with main earth connected to it and MET and again get a reading (still parallel path) but as soon as test with main earth only I get no reading?...customer contacting supplier tomorrow but am I missing something or have the DNO lost the earth??
 
When you say no reading what do you mean?
Does it go over scale eg greater than 1999 ohms or just read 0 on the display?
Or does the meter not allow the test to be carried out due to a high voltage( 50 v touch voltage exceeded) on the earth?
 
When you say no reading what do you mean?
Does it go over scale eg greater than 1999 ohms or just read 0 on the display?
Or does the meter not allow the test to be carried out due to a high voltage( 50 v touch voltage exceeded) on the earth?
He's testing external impedance.....live.
Seems like a supply fault.
 
thanks for replying Ian, my meter flashes 0 v and the reverse polarity light flashes, so I can’t perform the high loop test function but as soon as I move the clamp from the disconnected main earth and put it on the MET (all other bonding in place) the reverse polarity light goes green the voltage reads correctly and I get a reading of 0.14,so reading is fine it’s just not through the main earth (I think the polarity light in this instance indicates that all three probes are not attached ie when on the disconnected main earth it’s not going anywhere) never experienced it before
 
He's testing external impedance.....live.
Seems like a supply fault.
Yes I get that..
I was asking the reading displayed on the test instrument
[automerge]1580055448[/automerge]
thanks for replying Ian, my meter flashes 0 v and the reverse polarity light flashes, but as soon as I move the clamp from the disconnected main earth and put it on the MET (all other bonding in place) the reverse polarity light goes green the voltage reads correctly and I get a reading of 0.14,so reading is fine it’s just not through the main earth (I think the polarity light in this instance indicates that all three probes are not attached ie when on the disconnected main earth it’s not going anywhere) never experienced it before
Sounds like a fault with the means of earthing into the installation
[automerge]1580055737[/automerge]
You mentioned testing the sheath of the dno supply but with parallel paths in place,have you tried testing it on its own, parallel paths removed?
 
Last edited:
Yes tried that as well and again reverse polarity/no reading which points to supply issue I assumed
[automerge]1580055948[/automerge]
I’ll update once I be spoken to customer/DNO...
 
The sheath (do you mean lead?) is the DNO 'main earth' conductor if TN-S (Max Ze 0.8ohms)
Yes mate the lead sheath but initially I disconnected the 16mm main earth cable from the met and clamped on to it to get my readings and nothing so as discussed above I also clamped on to the sheath/DNO earth and still nothing unless I left the main earth connected to the Met and the sheath then I’d get a reading but obviously not true as it’s reading parallel paths..
 
Sounds like a supply fault, had a few myself locally but usually high Ze readings.
Recorded 137ohms on one installation for a TN-s (Max 0.8)
DNO sorted it.
DNO your best bet.
 
Sounds like a supply fault, had a few myself locally but usually high Ze readings.
Recorded 137ohms on one installation for a TN-s (Max 0.8)
DNO sorted it.
DNO your best bet.
Thanks mate yep customers onto DNO tomorrow, strange my readings were so low then? Always consistent at 0.14-.015...
 

Reply to No Ze through main earth?... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
417
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top