Hi,
I'm curious to get peoples opinions on this non domestic situation please:
I vaguely remember reading something that, if a cable is loaded to less than 30% its CCC, grouping can be ignored. In this instance the circuit is feeding a door access control panel with a negligible load.
Thanks
I'm curious to get peoples opinions on this non domestic situation please:
A 20A SP&N radial
Fed from a 20A MCB
70 degree singles, grouped in metal trunking fails with 2.5mm singles and even 4mm singles.
I vaguely remember reading something that, if a cable is loaded to less than 30% its CCC, grouping can be ignored. In this instance the circuit is feeding a door access control panel with a negligible load.