non rcd sockets pir coding | on ElectriciansForums
Discuss non rcd sockets pir coding in the Australia area at ElectriciansForums.net
mcm
What would be the best code for sockets that are not rcd protected?
No sockets are outside or near the doors so would it be a code 4?
The supply is a tns with 10mm bonding to gas and water but no rcd protection to any circuits.
code C3.. IMO. although not close to doors, an extension lead could easily be run outside. some may say no code if the installation pre-dates 16th.
You would in many cases use both C3 for lack of RCD protection for socket-outlets intended for general use by ordinary persons, and C2 for lack of RCD protection for socket-outlets used to supply mobile equipment outdoors.
Obviously if the installation is a flat on the top floor of a tower block, it is unlikely that there will be ant socket-outlets used for mobile equipment outdoors.
Reply to non rcd sockets pir coding in the Australia area at ElectriciansForums.net
Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
davesparks
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks