Non Registered Spark wiring NewBuild | Page 2 | on ElectriciansForums
Discuss Non Registered Spark wiring NewBuild in the UK Electrical Forum area at ElectriciansForums.net
Wales
Hi all
Went to a Newly Built Granny-Flat last week on behalf of MK's Switch Exchange Program
Opened the CU to find
  • spaghetti Junction,
  • No Labels,
  • Tails half out of Main Switch,
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat - (Don't know why 3)
  • No Bonding anywhere
Certificates:
  • No Property Name
  • Customer was the building company
  • Ze results mixed with Zs results
  • Non-Body Certs
  • No Signature on bottom of Certs
Gave the Electrician a call - details found in designer section only - asked for his registration number - reply "C&G 2382 and C&G 2391 I think!"
Asked for NAPIT, NICEIC, etc - reply what are they!
He recalls wiring the house - he didn't know he had to be registered
Called LABC - their reply:
  • No Building Control Certification
  • No Building Control Notice for Electrics
  • No Building Control Notice for Gas
  • No Building Control Notice for Insulation
  • No Building Control Notice for Windows
  • No Building Control Notice for ANYTHING!
  • Only thing they could find was Planning Permission which the customer applied for
Customer spent £85,000 for this build
Electrician is from Manchester Area - Worked down in Pembrokeshire, Wales on this one job
I don't know if I can post the name of the construction company or Electrician - MODs advise please
So you are saying only 3 cores of the SWA connected into the switch?
Does the 16mm suffer volt drop outside of the permitted in BS7671
What regs for SWA buried has to have a earthed sheath? TT on a outhouse, all they have done is extended the PME zone. Perfectly acceptable. Have you proven the metal pipework is a extraneous conductive part?
Ok so bad design on the showers.
this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.
[ElectriciansForums.net] Non Registered Spark wiring NewBuild
It was very similar condition to this one just bigger - 21Way MK CU - Split Load
This picture is taken of one I attended for British Gas Home Assistance
Originally Posted by Dillb [ElectriciansForums.net] Non Registered Spark wiring NewBuild No labels- hardly going too do any harm to anyone is it
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
Tails not in properly - and not cut tidy - only 3 cores connected!
16mm SWA- What problem here?
50m Run - Preferably 25mm would have been better to avoid voltage drop! ....Better maybe, but that's not saying it doesn't comply!!
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
SWA Buried underground Is, or has the SWA been earthed at one end only ''outgoing end''??
PME- DNO responsibility? Although no problem with extending it
Regs State this must be TT .....REALLY THINK AGAIN!! Better still name that Reg?? lol!!
50 MCB- sounds like it is doing its job properly
RCD Discrimination ...Not actually against any regulation
3 showers- No problem here
if 2 Showers Running - MCB Tripps - 4 Bedrooms for all family members - usual situation for this customer .....Is this a Granny flat or a 4 bed house, ... make you're mind up??
No bonding- are there any extraneous conductive parts?
All Pipework is metal .....internal maybe, but what of the pipes entering the property, these day's plumbers tend to use plastic for everything??
This building is 50m away from the main house! The Pipework is connected directly to a well!
You cant just extend a PME supply in this means - trying to find Reg now
One last time, i am repeating myself here. Is the metal work a extraneous conductive part? have you tested to prove it one way or the other?
Yes I have!
Ze between 100 and 200 ohms - acting as an earthrod
in regards to SWA - Armour is jsut cut and tapped at both ends - no glands
Inner insulation just passing through a 20mm hole in Iso in Main House - no supporting clamps - no earthing clamps
In House SWA is cut - only earth Conductor over 10mm is the 3rd core of SWA
2 x 30mA RCDs in Series
So you livened the house up without the main earth being connected?
What was your IR result when you tested between the main incoming earth and the metal work?
- - - Updated - - -
Yo have left lots of information out of you OP.
- - - Updated - - -
Like I said I went in to change Main Switch
Main Earth is connected via 3rd Core in SWA - its the Armor at Fault
Didn't IR - Installation Isolated and advised to get an electrician to repair work
Part of the MK contract is Im not allowed to offer my services to do work for these customers
Property owner is a retired Electrician (15th Regs) he had not looked in the CU ever
Nor had he checked any work - he relied on the Electrician being qualified and registered
I know i left lots out on my OP - sorry
Wish I had taken Pictures now! - Hind Sight is wonderful
- - - Updated - - -
I have a feeling the OP may have been registered before under a different name.
Never only this name sorry to disappoint you Dillb
Reply to Non Registered Spark wiring NewBuild in the UK Electrical Forum area at ElectriciansForums.net
It applies to commercial if it shares the same supply as a dwelling.
Recommended Sponsor News
Hi everyone,