C

cyko

Ok, here it is.

Im currently working on my collage project and Im a little bit stuck with cable sizing selection of protective device on a 3 phase system.

Im not looking for answers here, so im not gonna post any numbers, just a push back on track.

Does anyone know, off hand, the equations for this?

Any help would be greatly appreciated.

Paul
 
To start with don't forget that design current (Ib) is different for 400V.

(Ib) = P/(√3xUL)

Then select (In), In>Ib (or equal to)
Then calculate (It). You will first need to know the reference method, and any other correction factors you may need to apply (insulation, ambient temperature, grouping etc).

It = (Ib or In) / CaCgCiCcCf

It>In>Ib (or equal to)


With (It), determine (Iz).

When obtaining (Iz), obtain (mV/A/m).

Then assess and verify volt drop.

vd=((mV/A/m)xIbxlength) / 1000​

If within tolerance, then the (Iz) cable size is your result.


Then, depending on the level of your study, you can go on to determine thermal withstand and shock protection.
 
Last edited:
Thanks guys, think it was the root of 3 that i missed.

Assuming the rest is the same as the single phase method i should have it sussed now.

Thanks again
 

Reply to Not Cheating, honest in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
603

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top