Evening everyone

Had to re post as I started a post within a post:grimacing:

here's hoping I'm posting in the right part or I have started off on the wrong foot.
Long story
Asked by a friend to look at his friends electrics as the kitchen ring was tripping the RCD.
New colours cable
on 32amp B MCB
one of only 3 on the this bank protected by an RCD
5 double sockets
plus a bank of 6 FCU's

Before I went there I had him remove all the plugs plus and turn off the FCU's
believing that this would help narrow down the problem.
But it did not.
so drove to Leytonstone about 45 mins from me
where we split the ring at a double socket and we believed that we had found a the problem which was a bit of cable in the wall between one of the FCU's and a socket in the cupboard.
all this time the other leg was working fine.
So we managed to replace the cable and we seemed to be on the home stretch, when the other leg started to trip I been there for about 5 hours and it was 9pm by now so turned the ring into a radial thinking this will do until I get time to investigate further.
so left at 10:30pm and everything seemed fine only to get a call today saying that the MCB had tripped but not the RCD and thoughts apart from run.
 
Tut, tut....kitchen faults. OP's head 'll be spinning. Start from scratch. Check at all sockets for direct spurs or even JB's behind units. Disconnect all sockets and FCU's...(neons). Test each leg after each disconnection. You don't mention any continuity testing.
 
Anything outside any external sockets or flood lights?
Tut, tut....kitchen faults. OP's head 'll be spinning. Start from scratch. Check at all sockets for direct spurs or even JB's behind units. Disconnect all sockets and FCU's...(neons). Test each leg after each disconnection. You don't mention any continuity testing.
from short leg which we believe goes straight back to the board we are getting continuity on the L and E
 
from short leg which we believe goes straight back to the board we are getting continuity on the L and E

When you say continuity, do you mean end to end on the cores or from one to another?

And what about the neutral?

I would do IR tests from both "ends" of the leg .............

what were the R2 readings for each of the L, N and CPC before you took the ring apart?
 
When you say continuity, do you mean end to end on the cores or from one to another?

from one another


And what about the neutral?
neutral to earth ok
neutral to live ok
only getting it on live to earth

I would do IR tests from both "ends" of the leg .............

what were the R2 readings for each of the L, N and CPC before you took the ring apart?
from one to another
 
Maybe its time to call it a day. Fault finding takes years of experience to master. Why not be honest to your friend and say its above your level. Nothing wrong with knowing your limits and holding your hands up to admit it. Get the guy to get an experienced sparky in to locate the fault and explain where and how he located it. Use this as a opportunity to learn.
 

Reply to Nuisance tripping after splitting a ring main in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
919

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
451
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top