O
Octopus
All, I'm up for suggestions re the following "case".
House had nuisance tripping - did fault finding but didn't find anything conclusive. Issue for the home owner was that the single RCD was betweem the DNO and consumer unit so when it happened they lost everything and over Xmas this was happening every 10 minutes or so (so they said). Interestingly even though the tripping seemed to be mainly the "fault" of one circuit it could be set off by 4 out of the 7 circuits (I'd asked them to keep notes!)
Because the house is very old with various additions, I recommended a consumer unit change to a fully loaded RCBO set - with a caviat that it wouldn't remove the issue, more like narrow i down to a circuit.
Yesterday I installed the new consumer unit and did another full test of the house, the readings were almost the same as the previous set.
As the day wore on the dowstairs lighting circuit started tripping - and got worse as the day got darker.
No other circuits were tripping.
The only other variable was that it had been raining. Previously the owner had said that heavy rain didn't seem to affect it but horizontal rain or thawing snow did!
I could only get it to trip using a switch position which is one "4 gang hamilton" moduled set of dimmers.
So could the dimmers be the partly responsible? or moisture behind the switch? (none obvious) or a connection between the switches and the sets of lights?
One other thought was to remove the RCBO and install a MCB in its place??!!
Any comments, questions or suggestions would be welcome![Eek! :o :o](https://cdn.jsdelivr.net/gh/twitter/twemoji@14.0.2/assets/72x72/1f631.png)