Sorry for the Lenghty post, in summary. swapped RCD's on a split load board it stopped trippng. Why's that?
Got called back to Air Source Heat pump install that was experiencing nuisance tripping 2 days after a PV install.
It was a split load Eaton board with 2 of the heating circuits tripping on the one side and 1 other circuit and the sockets on the other side,
tripping the same RCD.
Had a look at all the terminations on the heat pump side, they were ok. I treid the sockets and it was every socket that was tripping so thought it was unlikely to be an equipment problem. I thought it might be a faulty RCD so I swapped them over to try and get the same results. Suddenly, no tripping?
The PV installers had chopped things up inside the board a bit, to get there stuff in and I noticed they had a bit of a flash, you can see the blacking but can't see how if it had been damaged that would stop the tripping once i swapped it?
Any thoughts my esteemed friends?