Observations please? | on ElectriciansForums

Discuss Observations please? in the UK Electrical Forum area at ElectriciansForums.net

FatAlan

-
Trainee
Nearly Esteemed
Supporter
Joined
Sep 16, 2016
Messages
2,065
Reaction score
1,993
Location
Surrey
Remote barn conversion? Largest SWA is incoming supply. Yet to establish where meter is :rolleyes: Getting a Ze at this point of about 58 Ohms.
 
[ElectriciansForums.net] Observations please?

Here’s the pic that I thought I’d uploaded!
 
Assuming this is fed from another building? So this would be a distribuition circuit giving you Zs or Zdb? Where are you measuring from? If you have checked the SWA gland and banjo and fly lead are all secure (you could pull the shroud away and try and get a measurement from the actual armour), then it must be either damaged cable or a problem at the other end.
[automerge]1583573785[/automerge]
Seems odd to earth that DB with a fly lead to the trunking when there is an earth terminal in the isolator next to it. Where do the other phases go?
 
Cheers Shaun. Installation is about 16 years old and from what I’ve seen, pretty shoddy. I’m told the supply comes from a pole and the meter is in a box in a field about 100m from the house.
 
Whenever I see cables such as these where you can see the spirular pattern of the stranded cables exposed on the insulation I can't decide if that is thermal degradation or just how the cable is. What do others think?
P.S. did you have ATT. on or off?
 
The larger SWA is the feed in and goes to the block which then feeds that 100A fused isolator that then feeds out on the next largest SWA to another RCD protected DB doing most of the circuits in the house. Theres another feed from the block to the DB top left that does a couple of circuits in the utility and hall area.
 
Told that it is a TT arrangement. ATT was off, I disconnected the main earths to the 100a switch and DB you can see in the photo and basically measured from the switch and the bonded bolt on the metal trunking where the 16mm main earth is attached. Isolated location with gas via bottles and plastic pipe water supply.
 
As its a SWA and there is no meter this is obviously a private supply. You say it comes from a pole so it must be a private OHL. There will be lots of connections all the way back to the source so I would be checking them, I would also consider TTing it.
 

Reply to Observations please? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
460
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
949
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
895

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views