Hi all, Do you guys and girls make observations on the fire detection when you do an EICR? If so how do you code it? I've always observed shortfalls in fire detection on an EICR and coded it seperately as 'FIRE' but I was chatting to another sparky the other day who incorporates his fire detection obs into the normal C1, C2, C3, FI coding system. What's your opinion?
 
Of course I agree that we should always work to better ourselves, but I don't agree that we should be mixing up 2 different standards into 1.
By this I mean BS5839 and BS7671.
If a landlord is responsible for the maintenance of both the fire detection and alarm systems, and at the same property, the general electrical installation, then that landlord should be aware of the need to employ competent people who are skilled in both disciplines. And that such people should also have the full knowledge required, along with the correct forms of certification required for each type of system being inspected and tested.

Which may mean getting 2 different contractors in, ie a fire alarm engineer, and an electrician.

In some cases (though in my experience, not many), both tasks could be accomplished by the same contractor. But as I said before, there will be 2 different, distinct, forms of certification and/or reports, with very little crossover between the 2.

In my opinion....
I get what you're saying. If the person undertaking THE EICR doesn't have knowledge of, or familiarity with 5839 etc then obviously there is less chance of any of those systems being codes as part of an EICR.

I can see why the codes (560.x) are there but they do require additional knowledge.sayibg that 7671 says itself that it may be supplemented with additional standards and documentation so I guess that also helps bring in other standards to the ballgame, whether they should be included on an EICR is a different matter but I am enjoying the discussion.
 
Indeed it's interesting to see how others interpret things.

I think we're in agreement @Lister1987 that anyone undertaking any kind of inspection and testing ought to be competent and experienced in whatever it is they're inspecting and testing.

And although it's correct that BS7671 does refer the inspector to several different standards and regulations outside of BS7671 that may also be applicable, and in some cases, supercede BS7671, I don't take the intent of that statement to mean that we as electricians are expected to be fully conversant with any of those other regulations. But rather that it may be necessary to advise that other specialist contractors may have to become involved in some installations, even in the Domestic sector.

I guess it depends on the nature and complexity of the installed systems, in this case, fire detection and alarm systems, as to whether the inspector is competent and equipped to carry out such inspections.

But I make the same point, just for emphasis, that an EICR is not the correct form to be noting such things. (Other than where they connect to the mains wiring).

I suspect I'm beginning to ramble now. Time for bed. ??
 
In answer to your question; none because I have yet to undertake a single one and so it's all hypothesis until such time I'm competent enough to under such works.

Grade F system (battery only - Fixed or replaceable), if any detectors found to be dead then I would C2.

Grade D System where, mains is present and working bit alarm is past battery expiry date I would C3 if other detectors were on the same level, otherwise if the next functional detector is above/below the current level then I'd C2 as you're losing the early warning that an alarm on the same level provides.

If the same system (Grade D) had faulty mains but working battery, again I would C2 or C3 depending on any 'local' backups.

MIs would also influence the coding as the BS EN standard would dictate exactly how that alarm should perform on mains and/or battery and if that manufacturer can't guarantee if Thier items will work with 1 or the either power sources missing.

With regards to -1 systems, in comparison with -6, I would code along a similar vain, I would also pull on the FSRRO and cite from that as you're then talking statutory duties, as opposed to a non-statutory product standard. You'll find they tend to sit up when you start bringing EAWR/FSRRO into your report as THAT is what most commercial/industrial entities will be familiar with, most tend to have a dedicated SHE manager or department, which if any good, would welcome your forensic analysis of not only BS7671 but also any overlapping 5839/1838/5266 observations.

That's me anyway, probably over the topby some judgements bit I'm satisfied with it.
If there is no physical wall to mount a call point or to run cabling (chased or containment), consider a freestanding self contained job.

View attachment 84379

A note of caution; I have been able to find no information regarding this products compliance with BS EN 54-11, possibly because it's not really a call point but I wouldn't be happy unless I had something in writing from the manufacturer - That said if you read the datasheet/manual they basically say we take no responsibility whatsoever as to whether the product will work or not, to me seems a bit underhand, I know most have something similar but they seem very specific with it.
A bit embarrassing then when you post this in another thread as a solution to a problem what would you code that as
 
Unless the fixed wiring tests show faults and/or the fixed equipment is damaged to the point it breaches IP ratings then it none of my business.

Same with emergency lighting, gas shut off systems, panic alarms and a plethora of other safety systems attached to the fixed wiring.

Coding/noting comments on an EICR just muddies the waters, if a business owner has a legal duty to have all these systems installed then they have a legal duty to have them maintained and tested.

So, say you note a none functional smoke detector on your EICR and the landlord replaces it, two days later the house burns down, all in the house die, as the radio link failed.

The landlord uses your EICR as proof he had been maintaining and testing his system. The court looks to you?

Leave well alone and concentrate your attention on the the things you are responsible for.
 
The purpose of regulation 560.10 is to make you aware that you install a fire detection system to the correct British standard , in this case BS5839 part 6, not to use it as a regulation number for out of date smoke detectors
 
The way I look at it is when you step outside the reach of the EICR the coding system does not apply, say you are testing the landlord section of a HMO and it has an obvious issue with a damaged cable to a call point, technically it is all part of the electrical installation but I would argue the F/A unless it is a old mains system would not be subject to the EICR, at most you could report on the condition of the supply to the panel.
As others have said, if you start making comments then you need to agree to this with the client and it wouldn't be included as part of the EICR either, F/A reports and documentation will need to be a separate inspection report and will need filing different, it also does not follow the coding system applied to an EICR, you better have full knowledge and understanding of the BS standards surrounding F/A design and installs as well as the changing recommendations we see as time goes by.
Lets just consider for 1min that you comment on a damaged sounder in a corridor and the landlord responds on it and you replace it, what if a fire occurs and a faulty smoke detector fails to operate the system, someone is badly injured or dies - think of the landlords defence team then asking what your understanding of the BS5839 is and why you gave the impression the EICR covered the F/A system by implementing recommendations and repairs to do on it.. this is a legal minefield and no one wants responsibility for a fatality so be careful you don't set yourself up legally for a big fall.
Your average HMO for example would often have weekly tests where call points or detectors are activated in rotation and at least a full annual inspection, I have one where I do 2 annual tests but half the install given its size so it is covered throughout the yr, no way would I inspect and report on the install without full knowledge of relevant regulations to cover it, so why would you entertain the idea when doing a EICR unless you are fully knowledge in such regulations, again the customer may get a false sense of security and a misguided view the system has been fully inspected, this could lead to a routine inspection been missed or delayed.
 
What exactly do you mean by shortfalls?

An out of date or missing smoke alarm as part of the electrical system I'm testing would be noted, a shortfall though lack of requisite alarms (if say a rental) isn't really in my scope although depending on your relationship with the landlord you may flag it up.
 

Reply to Observing fire detection shortfalls on EICRs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top