Second question of mine on here and it's one I've never got round to getting an answer for.


Mains comes into a building through a 60A main fuse for instance.
Why then are main switches rated at 100A or 80A?
Does this mean any load above 60A would blow the main fuse before it blew the main breaker?


Don't be harsh people. I'm fully aware the answer's probably an obvious one.
 
Last edited by a moderator:
Based on overload capacities then yes, I agree, but with the thought in the back of their mind that it has an overload capacity? Well, up until a year ago that was me. I'm time served and was taught this both at college and as an apprentice despite my reservations! I still designed my circuits based on the overload capacities of the OCPDs but always thought that stand alone RCDs had overload protection too. So I fully understand where someone is coming from who says they're qualified but don't know this.
 
Based on overload capacities then yes, I agree, but with the thought in the back of their mind that it has an overload capacity? Well, up until a year ago that was me. I'm time served and was taught this both at college and as an apprentice despite my reservations! I still designed my circuits based on the overload capacities of the OCPDs but always
thought that stand alone RCDs had overload protection too.
So I fully understand where someone is coming from who says they're qualified but don't know this.


one of my strongest memories of college is one of the tutors shouting to the class..."AN RCD PROVIDES EARTH FAULT PROTECTION ONLY.....IT OFFERS NO OVERLOAD OR SHORT CIRCUIT PROTECTION WHATSOEVER!!"

he must have drilled this into us about a dozen times.
 
I recall many years ago i did have my grey area's but they weren't what i would call the Basics so its this that worries me and as i said earlier i don't blame the student i blame the system thats been chopped down and simplified ...we had written exams as well as a small multi-choice and there was a high failure rate as well as a high thresh-hold before you were given a pass... nowadays i bet the majority would fail the same level of exam i took and out of the class of 22 only 5 passed ..... its amazing what a mess the goverment can do when ensuring more kids are in jobs hence we are where we are.
 
When I was training, it was quite common for many apprentices to fail either their practical training, college, or both. Nowadays with training centres pretty much guaranteeing a "pass", it's no wonder there are so many out there with little basic knowledge. No more sorting the wheat from the chaff.
 
The problem I found when I was at college is that we were being taught about different types of motors and their control before we'd even been taught ohms law! We were doing complex equations in year one and learning about bonding in year two! My education was back to front until year three so I definitely had my grey ares, but weirdly, had strong areas too. I learned basic ladder programming before I learned that an RCD had no overcurrent protection! I wouldn't say my education was weak, it just had weak elements. One or two tutors that had never been on a site in their life but then I had tutors who were absolutely excellent!My point is, it is very easy to know your stuff but at the same time have gaps in your knowledge. I did bonding to death at college, so I consider that basic knowledge, but I'm always stunned by the amount of qualified electricians who still get confused by it and think things like "it's there to stop the pipes becoming live if a cable touches them". Again, they have just had weak teaching in that area. I'm sure there are many people out there confused by bonding that DO know that a main switch is just a switch.The fact remains though that any spark worth his weight, if unsure will ask! It's the ones who think they know it all after 18 days but plough on regardless that worry me.

The best sparks are the ones that KNOW they have grey areas!
 
Last edited:
I understand what everyone is saying here but i give you 2 different scenarios totally then the kitchen ring with a 20a double pole switch connecting a socket for an appliance low level (thats wire theres a switch) years ago when touring some sidn off sites with my old niceic supervisor pointed out to me this was wrong and it needed to be a fused connection as the 20a dp switch was not rated to 32a is this correct I have seen this over the years a few times and noted it as a fault.

also say a 32a mcb then 6mm cable to an isolator 20amp rated iisolator 10amp load air con unit surely doing aan eicr on this the ciruit would need work to repace the isolator? or not potentially something could happen that lets more thn 20amps pull through the isolator surely the isolator has to be higher or equal to the protective device and not just rely on the fact the design current of the load is below the isolators rating or am i missing something
 

quote
my old niceic supervisor pointed out to me this was wrong and it needed to be a fused connection as the 20a dp switch was not rated to 32a




http://www.mkelectric.com/Documents/English/EN%20MK%20Technical%20Specifications/T02%20LOGIC%20PLUS%20Tech%20355-389.pdf


Use the link above and scroll down to page 13


MK Fused connection units and 20 amp double pole switches have exactly the same supply terminal capacity
terminal capacity suitable for 3 x 2.5mm conductors
. 2x4mm
. 2x6mm

A double pole swicth rating of 20 amp is the maximum rating of the switch contacts

Whether the device incorporates a 13 amp fuse or not,it will make no difference to the supply terminal capacity,they are exactly the same

If you are happy to accept the one, then the other should not be an issue
 
When I was training, it was quite common for many apprentices to fail either their practical training, college, or both. Nowadays with training centres pretty much guaranteeing a "pass", it's no wonder there are so many out there with little basic knowledge. No more sorting the wheat from the chaff.


i started writing a post highlighting this problem late last night, but i stopped halfway through because i was knackered.

at my college, failure wasn't an option. the college's funding was based on the success of the students.

i think i've mentioned this before, but i always found it strange that the really weak students (who really shouldn't have been accepted on the course) could fail some of the exams one week, and then get a distinction in the re-sit a week later.

in one of the online multiple-guess exams, one of the poorer students was sat at my '5 o'clock' - just over my right shoulder. throughout the entire exam, one of the tutors (who was supposed to be acting as an invigilator) was sat at the computer with him. when we'd finished i asked the lad what the tutor had been doing. he freely admitted that, whilst not giving him the answers outright, he'd been reading through the questions with him and had been pushing and prompting him towards the right answers.

i don't blame the tutors though. they were constantly under pressure (from the college hierarchy) to produce results. the same hierarchy that accepted these sub-standard students onto their courses.

it might sound harsh, but they should use a more stringent vetting process when they interview prospective students. you don't have to be einstein to be an electrician but you should be able to read & write and do a bit of maths.
 
I'm just totally gobsmacked at the total lack of common knowledge displayed on this thread by supposedly time served electricians. In fact i can't and don't believe that they are, not too sure if they are even electrical trainee's! God Help this Industry!!

My hat off to Darkwood & Telectrix for having the patience to go back to bare basics and spoon feed these guy's the why's and wherefores of the operation of a CU main DP isolator/switch!! I know i haven't that kind patience!! lol!!
 
i started writing a post highlighting this problem late last night, but i stopped halfway through because i was knackered.

at my college, failure wasn't an option. the college's funding was based on the success of the students.

i think i've mentioned this before, but i always found it strange that the really weak students (who really shouldn't have been accepted on the course) could fail some of the exams one week, and then get a distinction in the re-sit a week later.

in one of the online multiple-guess exams, one of the poorer students was sat at my '5 o'clock' - just over my right shoulder. throughout the entire exam, one of the tutors (who was supposed to be acting as an invigilator) was sat at the computer with him. when we'd finished i asked the lad what the tutor had been doing. he freely admitted that, whilst not giving him the answers outright, he'd been reading through the questions with him and had been pushing and prompting him towards the right answers.

i don't blame the tutors though. they were constantly under pressure (from the college hierarchy) to produce results. the same hierarchy that accepted these sub-standard students onto their courses.

it might sound harsh, but they should use a more stringent vetting process when they interview prospective students. you don't have to be einstein to be an electrician but you should be able to read & write and do a bit of maths.

In my day, we had to sit a series of aptitude and math tests to be accepted by my company as an apprentice!! There was no such thing as multiple choice C&G exam questions either. Each question if answered, needed to be answered in full, so if you didn't know, then you failed, it was as simple as that!!
 
By that definition Eng that makes me a Electrical Trainee. I find that rather offensive.

There was a time when you didn't know it all.

I can't help how you define what i've stated, or if you want to take offence or not!!

Yes, .....it was a very long time ago, but nothing as basic as knowing what a CU DP main switch is!! lol!!
 
So you knew that from birth did you? Wow!

You can help how I define what you've stated, and that is by not stating it. What you define as basic knowledge is completely subjective and even still, how can someone who was taught this most 'basic' of knowledge from the word go by more than one 'qualified' tutor and by his site supervisor be at fault for accepting what he was being told? I don't know the OPs situation, whether or not he is a Electrical Trainee or a time served spark, but what I do know mainly through personal experience is that questions like this can be answered without jumping to conclusions.

What I can't abide by is supposed 'qualified' sparks asking stupid questions like: "Why can't I use one neutral conductor for two different circuits?", "does the water need bonding if it comes in in plastic?" and "can you put a socket in a bathroom?" when the answer is there in black and white in the BGB. Unfortunately, there are things that aren't in the BGB that need to be taught, sometimes they just happen to be taught wrongly or not at all. There was a recent post on here from a valued member asking questions about adiabatic equations and how 't' is applied in different circumstances. This is basic stuff for me, calculations, formulae, thermal effects, inductance, capacitance, trigonometry, transposition blah blah... but clearly it isn't basic for him. Still, I know through some of the advice he has given others, stuff that is basic for him is good advice and that he knows what he is doing but most importantly, knows his limitations at this point in time. Should I be slating him for his lack of 'basic' (in my opinion) knowledge?

Like I said, I was learning ladder logic before I even knew about bonding! At the time I still thought that an RCD had overload protection (not that it affected my work at all) I was wiring and programming complex automation systems, fault finding motors and designing installations, but by your definition I would be a $hit electrician because I lacked 'basic' knowledge. Well sorry mate but we all lack a little basic knowledge here and there.

I refuse to accept that someone who can realise that they need to ask questions, however basic at times, must be crap at what they do!

I bet you couldn't tell me off by heart the minimum distance control gear can be placed from a swimming pool or basin? I know it, it's basic knowledge Eng!?!?!. Does that make you a crap spark? Of course not! :)
 
Last edited:
In my day, we had to sit a series of aptitude and math tests to be accepted by my company as an apprentice!! There was no such thing as multiple choice C&G exam questions either. Each question if answered, needed to be answered in full, so if you didn't know, then you failed, it was as simple as that!!

I think you've hit the nail on the head there Eng. Back in the 80's when I started my apprenticeship, you weren't even accepted as a trainee without GCE maths and physics, along with a day of aptitude tests just to see whether you could apply logic and common sense. Only once you got through that (about 25% managed it the year I started), then the 4 years of "fun" began.
Now you can go from being someone who can't tie their shoelaces to becoming "qualified" in 18 days!
Heaven help us....
 
No-ones saying we don't have grey areas, or grey moments, but when you need to be led by the nose step by step on the function of a DP switch, then i'm sorry that's very worrying and doesn't instill confidence in that person!!
And that's all i going to say on the matter, it's not worth the hassle...

Yes i do know!! Most of my projects involve provision of swimming pools etc where residential accommodation is included and/or indoor pools for medical purposes. Also know the recommendations that are applied by other international standards too, ...Yes they do differ.
 
when you need to be led by the nose step by step on the function of a DP switch

Well that is a little different to either thinking one thing or the other. If someone needs it explaining to them again and again then there are obvious problems there, some of which aren't electrically related if you know what I mean... But simply believing one thing, asking a question and then being put right isn't the same is it.
 
Every day is a school day, no mistaking. Thing is, during a long apprenticeship you would cover most of the basics and have a few grey areas to iron out as the years progressed. Nowadays, you can't possibly cover even the basics in a few weeks before being let-loose on peoples' homes. I bet that at least once a week I am still shocked that someone had the absolute bare-faced cheek to charge for what is frankly appalling.
I have no problem with what people charge, as long as the customer is aware up-front, but I find it utterly disgraceful that people who can't install a backbox level are being certified as "qualified". Surely, these training courses should at least cover the basic building skills which are essential for domestic work???
 
Hi all

Well done D Skelton

firstly I am a time served electriian i started in September 2001 and finnished in May 2005 with 2391 2006
I have a Agrade gcse math year 2000 and double AA Science
2001 Ihave physics as level grade d and mathematics grade e

I never asked about the function of main switch or wether a an rcd as overload protection or not I always knew they do not

However what I did believe is that any electrical componet not fused down in anyway making up the supply to aload had to be of equal value or greater (ampage) than its protective device and not merely designed so that you wouldnt exceed it current rating nobody answered is a 32a mcb using 6mm cable to a 20amp isolator feeding a 10/20amp whatever below 20amp load acceptable as the load is designed not to be above the 20amp isolator .

A
 
as far as i can see it this scenario is the same as a 100a main fuse supplying a db with 2x 80a rcd with the load split so you wont overload that 80amp and by overload i dont mean trip the rcd as it wont i just mean pull more than the components cuurrent carrying capacity

surely if this is ok then so to would the 32amp radial? I would have always said the isolator needed upgrading to 32amp and the circuit was not designed well for its intended use.

It was a simple question with a simple anser that I obviously had not had taught to me in this way I am mister careful and have always done very well whereever I have worked and dont not expect to be called a crap dumb electrician as this is definately not the case
 
so that scenario is ok? so what about then 32a circuit 1.5mm cable 5amp (whatever aplliance no fuse) that is again ok as the cable will not pull more than the load of that appliance?
 
So you knew that from birth did you? Wow!

You can help how I define what you've stated, and that is by not stating it. What you define as basic knowledge is completely subjective and even still, how can someone who was taught this most 'basic' of knowledge from the word go by more than one 'qualified' tutor and by his site supervisor be at fault for accepting what he was being told? I don't know the OPs situation, whether or not he is a Electrical Trainee or a time served spark, but what I do know mainly through personal experience is that questions like this can be answered without jumping to conclusions.

What I can't abide by is supposed 'qualified' sparks asking stupid questions like: "Why can't I use one neutral conductor for two different circuits?", "does the water need bonding if it comes in in plastic?" and "can you put a socket in a bathroom?" when the answer is there in black and white in the BGB. Unfortunately, there are things that aren't in the BGB that need to be taught, sometimes they just happen to be taught wrongly or not at all. There was a recent post on here from a valued member asking questions about adiabatic equations and how 't' is applied in different circumstances. This is basic stuff for me, calculations, formulae, thermal effects, inductance, capacitance, trigonometry, transposition blah blah... but clearly it isn't basic for him. Still, I know through some of the advice he has given others, stuff that is basic for him is good advice and that he knows what he is doing but most importantly, knows his limitations at this point in time. Should I be slating him for his lack of 'basic' (in my opinion) knowledge?

Like I said, I was learning ladder logic before I even knew about bonding! At the time I still thought that an RCD had overload protection (not that it affected my work at all) I was wiring and programming complex automation systems, fault finding motors and designing installations, but by your definition I would be a $hit electrician because I lacked 'basic' knowledge. Well sorry mate but we all lack a little basic knowledge here and there.

I refuse to accept that someone who can realise that they need to ask questions, however basic at times, must be crap at what they do!

I bet you couldn't tell me off by heart the minimum distance control gear can be placed from a swimming pool or basin? I know it, it's basic knowledge Eng!?!?!. Does that make you a crap spark? Of course not! :)


you make some excellent points here mate, especially about basic knowledge being subjective and hopefully i'll remember it the next time i jump down someone's throat. (but don't hold your breath!!).


having said that, when i think about your confusion over the role of RCD's, i realise that your mistake was borne out of misinformation. if you have your teacher and your gaffer challenging your beliefs, it's more than likely that you're going to be swayed towards their way of thinking.

what you say about "not knowing the op's situation" is a valid point, but try as i might, i can't imagine anyone telling him that the double-pole main switch on a domestic consumer unit is used to break overloads.

i've met a few people that struggled to get their heads around the role of a RCD, but i've never met anyone who thought the main switch was a MCB (on a domestic cu).
 
In my day, we had to sit a series of aptitude and math tests to be accepted by my company as an apprentice!! There was no such thing as multiple choice C&G exam questions either. Each question if answered, needed to be answered in full, so if you didn't know, then you failed, it was as simple as that!!


you were lucky; you entered the industry before the accountants started running the show. the quality of education shouldn't be sacrificed in order to make a profit.
 
I once worked with a sparky that had completed the apprenticeship and been in the trade, for the same firm, for over 10 years. I heard him on the phone one day talking to one of his mates. He was talking about a normal thermostat, in a house. He told his mate that the stat controlled the temperature of the rads!!! Of course after he finished on the phone, I corrected him but not in a billitiling way. In his defence, he did say that all he's ever been shown about stats, is how to fit em, not how they work! He has given me invaluable advice on stuff that Ive never come across before and thats what this game is all about...learning!

It comes down to how you were taught at college by your tutor and by your mentor (sparky), if they were good at there job, you SHOULD be good at yours!!!
 
I once worked with a sparky that had completed the apprenticeship and been in the trade, for the same firm, for over 10 years. I heard him on the phone one day talking to one of his mates. He was talking about a normal thermostat, in a house. He told his mate that
the stat controlled the temperature of the rads
!!! Of course after he finished on the phone, I corrected him but not in a billitiling way. In his defence, he did say that all he's ever been shown about stats, is how to fit em, not how they work! He has given me invaluable advice on stuff that Ive never come across before and thats what this game is all about...learning!

It comes down to how you were taught at college by your tutor and by your mentor (sparky), if they were good at there job, you SHOULD be good at yours!!!


to be fair, indirectly, they do.

if the air temp' drops below the thermostat's setting, then it fires the boiler which heats the radiators.

but i get what you're saying - they're not directly linked.
 
to be fair, indirectly, they do.

if the air temp' drops below the thermostat's setting, then it fires the boiler which heats the radiators.

but i get what you're saying - they're not directly linked.

Yes but he was saying, if you set the stat to say, 25*C, then thats what the radiator temperature will be at.....but the radiator temperature is controlled by the TRV.

As I said, its just miss/ill information from his tutor/mentor.....but then again, this may have never come up over the 4 years!!
 
he didn't work for bailey's did he?

everyone i meet from there seems to spend their entire working life doing the same thing, day-in day-out.
 
When I was attending the 17th edition course some time ago, the tutor was telling us how he had an irate boss storm into one of his lectures to tear strips off him about something he'd told "his boys". For years this gaffer had told his boys that to test an RCD all you have to do is press the test button and the internal gubbins did all the calculations and tripped out if it was all hunky dory. He was very angry that the tutor had told them all that they need to use a piece of equipment to carry out testing...
 
Yes but he was saying, if you set the stat to say, 25*C, then thats what the radiator temperature will be at.....but the
radiator temperature is controlled by the TRV.

As I said, its just miss/ill information from his tutor/mentor.....but then again, this may have never come up over the 4 years!!


i've never bothered with those - never really trusted them. i just have the old lockshield valves.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Obvious question more than likely.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
76
Unsolved
--

Advert

Thread statistics

Created
jwc,
Last reply from
shagbite,
Replies
76
Views
5,851

Advert

Back
Top