Second question of mine on here and it's one I've never got round to getting an answer for.


Mains comes into a building through a 60A main fuse for instance.
Why then are main switches rated at 100A or 80A?
Does this mean any load above 60A would blow the main fuse before it blew the main breaker?


Don't be harsh people. I'm fully aware the answer's probably an obvious one.
 
Last edited by a moderator:
On a similar vane I had an electrician with 2391 who carried out a PIR and recommended that a 40A 30mA RCD should be changed to a 32A one, asked him why he replied because the fuse protecting the circuit is only 32A thus it would go before the RCD if the was an earth fault and not the RCD as it was rate at 40A, shook my head and walked away in disbelieve
 
There is a simple reason for switches being 100A.... They can be used on a system with a 60A fuse, an 80A fuse, or a 100A fuse. In other words, one size fits all.
As already said, a switch is just that, the same way as an RCD is just that...they do not "trip" on overcurrent. While I agree that nobody knows everything, this is pretty basic stuff.
 
I was refraining from saying anything, but it seems like the rest of you haven't held back! I agree with jamesBoater. how can the OP not know this basic knowledge after having gained said quals?!
 
Thanks for the explanation, Darkwood. I've completed a full apprenticeship, AM2 and NVQ Level 3. Everything's much clearer now knowing that the main switch is exactly that... A switch.
FFS and people on this forum lambast Electrical Trainee!

Stick a 63A Main switch in and everyones happy?! ;)
 
a lot of domestic propeties have a 100a main fuse so why do many domestic boards have 100a main switch then 80/63a rcds surely there is potential for overload under fault conditons or am I missing something silly?
 

Reply to Obvious question more than likely. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
696
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top