D

denelectrics

Hi folks. Called out to micro tripping rcd occasionally. Customer bought new micro, but that is doing the same. I said, get the new one replaced ...just in case, which he did. Still the same. Only ever happens with the micro
Tested rcd and n-e, l-e, rcd testing ok on 0.5, 1X and 5X. Cant remember the figures, but tested fine.
Kitchen ring circuit n-e with washing machine and dishwash (both on d/p spurs) down to 150mohms with d/p switches on. 250mohms with d/p switches off.
Socket tests ok and no nipped neutrals anywhere. All other appliances test ok (not tested defrost on f/freezer yet)

Suggested he try micro next time with washing mach and dishwash switched off at wall, just to see if any difference.
Its still the same.

Cust wanting me to replace rcd, just in case.

Any suggestions.
 
if after ramp test there is still no solution why not put microwave on it own specifically labelled circuit and label socket MICROWAVE ONLY...on non rcd side obviously
So what happens if the micro wave is faulted and leaking excessively to earth you are now leaving the premises in a more dangerous condition so IMO that is a definite no. The RCD is there for a reason and trips for a good reason if not faulted. Remember the IET guidelines for leakage are .75mA Portable or hand held & 3.5 mA other class 1 equipment !
 

Reply to Occasional rcd tripping with microwave. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
692
davesparks
D
And fully tested it with an MFT obviously
Replies
9
Views
276

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top