Just finished a domestic EICR where I found the cooker isolator to be smack bang in the middle of the actual cooker position.
The oven had a glass lid which, when lowered, automatically isolated the supply to the hobs.
I have noted it down as C3 due to the existing cooker lid covering it but, on reflection, I think I may be wrong on this and a C2 may be required.
The cooker isolator is on a tiled kitchen wall and significant destruction would be needed to move it which I doubt the landlord would entertain without a fight.
Where do I go with this? I know the regulations state that the isolator should be positioned at least 100mm from the cooker edge but this thing is right in the middle!!