Hi all.

Just finished a domestic EICR where I found the cooker isolator to be smack bang in the middle of the actual cooker position.
The oven had a glass lid which, when lowered, automatically isolated the supply to the hobs.
I have noted it down as C3 due to the existing cooker lid covering it but, on reflection, I think I may be wrong on this and a C2 may be required.

The cooker isolator is on a tiled kitchen wall and significant destruction would be needed to move it which I doubt the landlord would entertain without a fight.

Where do I go with this? I know the regulations state that the isolator should be positioned at least 100mm from the cooker edge but this thing is right in the middle!! 😖
 
I know the regulations state that the isolator should be positioned at least 100mm from the cooker edge but this thing is right in the middle!! 😖
Do they? I'm not defending it as suitable for the environment, or compliant, or anything like that, but where have you come up with this arbitrary distance of 100mm?
 
Do they? I'm not defending it as suitable for the environment, or compliant, or anything like that, but where have you come up with this arbitrary distance of 100mm?
I clearly just made stuff up out of thin air didn't I based on my poor interpretation of the regs......😔

Ok, so there is no specific regulation for its positioning but it is clearly in a position where potential for heat damage.
I am happy to C3 it but as it is Private Rented, I need to cover my back.
 
There might be some examples given in one of the IET's Guide Notes as I do remember seeing something (not got them to hand just now).

Also there may be requirements in the building regulations, but I don't know.
 
"Part P of the Building Regulations states that there should be no outlets or accessories (cooker hoods excluded!) above any type of hob, nor within 300mm of the edge of the hob. Any socket outlet should be fitted so that it's centre is a minimum of 150mm above the top of the worktop.

In practice, the regulations may not be retrospective. Ie: If the existing kitchen was installed under previous regulations that didn't have the same constraints, then it may not be essential to move the socket outlet."

Extracted from an external source.
 
I'm pretty sure that part p (or at least the approved document) doesn't say that. The Electrician's Guide To The Building Regs (my copy is 17th edition) shows a diagram saying no accessories above the hob, and min. 100mm to the side. It doesn't say which regs this comes from, so I assume it's guidance only
 
My copy of the 18th edition of "Electrician's guide to the buildings regulations" has this on page 70, section 5.2.3

(b) Cooker control switches, extractor fan switches, etc, should not be mounted so that it is necessary to lean or reach over gas or electric hobs for this operation.

(d) Accessories should be installed a minimum of:
(i) 300mm from the edge of kitchen sink and draining boards to reduce the risk of being splashed
(ii) 100mm horizontally from the edge of a hob
An accessory should not be located immediately above a hob due to the possibility of people reaching over suffering burns or the flexible cable of the equipment being damaged.
 
Last edited:
My copy of the 18th edition of "Electrician's guide to the buildings regulations" has this on page 70, section 5.2.3

(d) Accessories should be installed a minimum of:
(i) 300mm from the edge of kitchen sink and draining boards to reduce the risk of being splashed
(ii) 100mm horizontally from the edge of a hob
An accessory should not be located immediately above a hod due to the possibility of people reaching over suffering burns of the flexible cable of the equipment being damaged.

And the danger from falling bricks of course 😀
 
In all seriousness though, the way I sought the information I needed then, thinking it was correct without actually checking the facts first is actually a bit of an eye-opener for me. It has made me realise that I not only rely on those expensive books I've bought but, more importantly, I seriously NEED to get my head in them a bit more!!

I'm really annoyed at myself. I'm a professional electrician who takes pride in his work yet I fell at the first hurdle in this instance.

Gutted about it. 😔
 

Reply to Odd cooker isolator position in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Check the clearance between the back panel and/or terminal cover that you've removed. Look for small burn marks.
Replies
3
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top