Tested an RCD spur earlier with some odd results

Tested at x 1/2 (both waveforms) and no trip
x 1 (0 degrees = 28.5 ms), (180 degrees = 18.4 ms)
x 5 (0 degrees = 8.2 ms), (180 degrees = 40 ms)

S0 getting bang on 40ms at x5 on 180 waveform; i know its in limit but was expecting it to be (at least) as low as the x5 0 degrees result.

The supply is TNCS, the circuit has low Zs, testing carried out at rcd spur itself, with load side disconnected. Tried it with two different sets of leads and same result, the testers been recently calibrated.

What would you do in this situation ?? I realise the x5 result is within limits (just). Really im perplexed, if this result is due to the nature of the waveform, or if the RCD is iffy.

And to add to the mix im reading that x5 rcd tests are , strictly speaking only required where your max Zs values cannot be met.. e.g. TT installations.
 
Last edited:
Yeh additional protection against direct contact , x1 tripping times below 200ms would account for that where the circuit has a low enough ZS would it not ? I know the regs state x5 have to be within 40ms for TN systems too, but thats' backup to protect against a low high Zs scenario aint it
It’s got Nothing to do with back up of anything or a high zs.
A 100ma rcd would be suitable for a high zs on a TT for fault protection for circuits where additional protection is not required however it’s not a requirement to test a 100mA rcd at 5 x the rated current as it does not afford additional protection.
Only a 30mA rcd will offer additional protection and 40ms is the time given before an electric shock could become fatal.
Hence at 150mA it must disconnect in 40ms or less
Bs en 61008 rcds for 30mA
1x test for fault protection, must disconnect in 300ms or less
5x test for additional protection, must disconnect in 40ms or less
 
Last edited:
It passes....but ...only last Saturday I had to return to a job I had installed sockets on TT using a safetysure FCU...it had only lasted 2 years. Not fitting that again, they are a good price for a reason ...it will be a power breaker now.:rolleyes:
 
What has Zs
Aw right, will have to get my head round that, nice one. Where I was going with ZS scenario sounded right in my mind but hey ho potatas/potatoes , u learn something new every day :rolleyes:

Will an MCB operate at 30ma!

The RCD is being used for additional shock protection due to failure of basic protection/carelessness of user etc. it should operate before the end user receives a fatal shock.

The MCB offers protection to the cable.
 
What has Zs


Will an MCB operate at 30ma!

The RCD is being used for additional shock protection due to failure of basic protection/carelessness of user etc. it should operate before the end user receives a fatal shock.

The MCB offers protection to the cable.

Yes when you put it like that it all makes sense now. Feel rather sheepish now tbh to have made such a daft assumption. I mean the ZS itself wont affect the trip time will it :oops:. Will be reading up again on this subject and nail it.
 

Reply to Odd test results on RCD Spur in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top