Hi all, just wondered if one of the members could shed a light on my result of a Ze test. I have just changed my ccu in my ex council house in order to add 2 new circuits(mains powered smoke and heat detectors and also a mains feed for my alarm). The house was rewired about six years ago so the cables and fittings are in good condition and the correct sizes, but in the old colours. The ccu that i changed feeds all circuits in the house except for the electric storage heaters that are on their own ccu and operated by an economy 7 radio time switch. I have tested every circuit to BS7671 2008 (both dead tests and live tests). Everything seams ok and has been recorded on the apropriate cert, except for the Ze test. The 16mm earth to new ccu, the earth to the heaters ccu and the 10mm earth bonding to water(no gas feed in house) are all connected to the earth terminal enclosed in the TNCS enclosure which houses the 100amp cut out fuse. fortunatly ther is no seal on the cut out so i was able to remove fuse and gain access to the earth terminal to remove the other earth to do the test. I isolated the heater ccu before dissconnecting its earth. I then dissconected the earth from the new ccu and connected my megger1552 to the correct point and tested the Ze. The result i got was very low and caused some disbelief on my part( 0.07 ohms) as i was expecting around 0.34ohms. i did this test serveral time with the same results. The megger did indicate that ther was some Interference some where, but all circuits were isolated apart from the radio time switch so not sure if this result is valid. This has to be acuratly measured as this job is to be used for 1 of my assessments for self cirtification. Also the meter cables are the old colours is it ok as on is off meter and one off cut out (seald Meter). cheers
 
Hi there.

Are you saying you disconnected all other earthing conductors from the MET and left just the earth under test there by eliminating all parallel paths??

It could be that you are very close to a sub-station transformer and with it being a TN-C-S system the earth is very low.

What reading did you have for PFC?? was this high?? If it is the case I would expect a reading of around 3285A.
 
.07 is fine its quite common in my area to be low because you are never far from the transformer
the job in the photos in the show us your installs section i posted has ze of .10 and they were recorded by the dno and were happy
as lenny said just watch your ka reading
 
Thanks, yes i dissconnected all other earthing conductors from the MET. My PFC reading was 3.3Ka. As for the meter tails which are 25mm black and red do i need to change these as 1 is from a henley block which i could change and 1 is from the meter which has a seal on ang therefore not permissable touch. Thanks again, knowledge is power.
 
it the tails are 25mm dont worry about the colour. If you want to be correct wrap some tape round them to mark them. you dont have to change them. besides what means you got to isolate the main incommer to D.B ?
 
Cheers. The cut out has not been resealed since the house was rewired 6 years ago by some contractor working for the coucil. see attached pic of ccu,s.
 
HI everyone Just Ihad exam 2391, the question was many special location in domestic installtion?
My answer, was nine special location,is that right or wrong
 

Reply to Odd Ze test result. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
Thanks all for the suggestions! Customer doesn't store anything else in the cupboard with the tank, not even towels or sheets. Heatrae stat is...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top