I wonder if anyone can offer advice on storage heating circuit design.

I have a job to replace two BS3036 fuse boards, with 17th Edition consumer units. One of the boards will manage the existing storage heaters for the property, currently three heaters, old & no idea of size but each fed via 15amp fuses and 3kw immersion heater. This board receives an 'Economy 7' supply. The property also has 8.5kw electric shower, fed from the standard supply.

My client wishes to increase the storage heaters from three to six. The property has a 100amp supply. Clearly I will need to calculate the new demand, but even just basing it on 2.5kw heaters and the immersion, that is 64amp approx. If the client uses the shower at the same time as the heaters receive their charge, that is approaching 99amps.

I have already advised my client, but if I install 6 x 16amp circuits, there is potential to overload the DNO fuse.

Never installed an off peak board before, I've considered having a DP MCB as a main switch to prevent overload of the DNO fuse, or is it just case of calculating maximum demand for the normal tariff board and limiting the number of off peak circuits?
 
I know this is a more expensive alternative but you could talk to the customer about the benefits of installing an electric boiler with a wet system. It offers so much more flexibility of heating a home and can provide heat whenever it is needed and/or wanted.

The boiler itself could most likely be installed in the same place the existing cylinder is now.
 

Attachments

  • image.jpg
    image.jpg
    81.2 KB · Views: 156
Last edited by a moderator:
I wonder if anyone can offer advice on storage heating circuit design.

I have a job to replace two BS3036 fuse boards, with 17th Edition consumer units. One of the boards will manage the existing storage heaters for the property, currently three heaters, old & no idea of size but each fed via 15amp fuses and 3kw immersion heater. This board receives an 'Economy 7' supply. The property also has 8.5kw electric shower, fed from the standard supply.

My client wishes to increase the storage heaters from three to six. The property has a 100amp supply. Clearly I will need to calculate the new demand, but even just basing it on 2.5kw heaters and the immersion, that is 64amp approx. If the client uses the shower at the same time as the heaters receive their charge, that is approaching 99amps.

I have already advised my client, but if I install 6 x 16amp circuits, there is potential to overload the DNO fuse.

Never installed an off peak board before, I've considered having a DP MCB as a main switch to prevent overload of the DNO fuse, or is it just case of calculating maximum demand for the normal tariff board and limiting the number of off peak circuits?

There not many people who'll have a shower after midnight!
 
Maximum off peak load is normally 80amps
normally 3 sizes of storage heater(bathroom heater can be smaller)
Dimplex heater sizes
small 1.7kw
medium 2.55kw
large 3.4kw
immersion heater 3kw
Ps:- these ratings were the same when 240v was used for calculations
as long as the house has a mixture of sizes of heater then the loading should be ok
 
There not many people who'll have a shower after midnight!

But maybe early morning!

Worth asking what are the chances of all the storage heaters actually being turned on? Let alone on full blast.

As a (slightly long winded) example - I live in a moderately sized 2 bedroom rented flat (spread over one floor) with 2 storage heaters - Hall (XL18) & Lounge (XL24) There is panel heaters in the bedrooms, plinth heater in the kitchen & fan heater in the bedroom. Currently we only have the Lounge one about 2/3 of the way, with leaving the doors open throughout the day it provides enough heat for the entire flat (around 20 deg). Through the winter we had the hall one on too (also being around 2/3 on) this kept the place warm over the worst of the cold no bother. The only time we have used any of the other heating is on the odd night recently when it's been colder stuck the panel heater on in the wee ones room (she won't sleep through if it's not bang on 20deg!).

Think I worked out it costs us about £3 a day to heat the place through the winter (both heaters on with occasional panel heater too).
 
The heaters will all be operating on their thermostats once it's reached the early hours of the morning so the current demand won't be anywhere near as much as the initial couple of hours
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Midwest

Arms
-
Joined
Location
Oxfordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Off Peak Heating - Circuit Design
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
Midwest,
Last reply from
Leesparkykent,
Replies
15
Views
3,345

Advert

Back
Top