Went to look at a job today, place is about 30years old and has Wylex rewirable fuse board (timber one at that), 16mm tails on a 60A fuse, 16mm main earth (on PME) and 10mm water bond. At some point over the years a oil fired boiler has been added to the central heating to go with the solid fuel stove that's in the front room. Oil tank is in the back garden and the boiler is in the garage. The garage however is not accessible through the house and instead has to be entered from either the front drive or back garden. Is the garage therefore classed as being outside of the equipotential zone? Reason for asking is due to the lack of bonding to the oil pipe, is there none because it's not required (due to being outside the equipotential zone) or because of laziness?
Reply to Oil bond. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
4K
Nothing wrong with it. Which manufacturers have you got this information from? What do you mean by trip speed? Fuses and MCBs can operate in the...
davesparks